Review the procedure for nulling the meter on a transformer turns ratio test set. 81% of technicians have missed this question.
Understand accuracy ratings for metering. Particularly, know how to calculate accuracy at points other than full scale. 74% of technicians do not understand these concepts.
Know the relative phase angle for a circuit having capacitive reactance and resistance. This question requires no calculation, just an understanding of the relative phase angles. 74% of technicians miss a question on this topic.
Study up on confined space. 67% of technicians do not know who keeps cancelled entry permits for a year.
Understand battery chargers and their role in a substation. In a correctly designed system, the charger must supply all load including indicating lamps and relay control power as well as maintain battery voltage. 63% of technicians believe that the charger provides current to maintain battery voltage and absolutely nothing else.
Research neutralization numbers for transformer oil acidity tests. 63% of technicians miss a question on this topic.
Note: 73 technicians took the NETA Level 2 exam in the spring of 2000. 29 passed.
Source: Official NETA internal memo from Rod Hageman, Technical Exam Chair to NETA Accredited Representatives dated July 21, 2000. Re: Spring 2000 Level II Certification Exam.
Understand accuracy ratings for metering. Particularly, know how to calculate accuracy at points other than full scale. 74% of technicians do not understand these concepts.
Know the relative phase angle for a circuit having capacitive reactance and resistance. This question requires no calculation, just an understanding of the relative phase angles. 74% of technicians miss a question on this topic.
Study up on confined space. 67% of technicians do not know who keeps cancelled entry permits for a year.
Understand battery chargers and their role in a substation. In a correctly designed system, the charger must supply all load including indicating lamps and relay control power as well as maintain battery voltage. 63% of technicians believe that the charger provides current to maintain battery voltage and absolutely nothing else.
Research neutralization numbers for transformer oil acidity tests. 63% of technicians miss a question on this topic.
Note: 73 technicians took the NETA Level 2 exam in the spring of 2000. 29 passed.
Source: Official NETA internal memo from Rod Hageman, Technical Exam Chair to NETA Accredited Representatives dated July 21, 2000. Re: Spring 2000 Level II Certification Exam.