What is the theoretical maximum symmetrical fault current that would be available at the secondary terminals of a 3-phase 12,470-480Y/277V, 1000kva, 6.25% impedance transformer?

I am having problems solving this question. Please advise.

SecondGen
June 23, 2015, 10:53 AM
Fault Current = Full Load Amps (FLA) / % Impedance (Z)
FLA = VA / L-L Voltage x 1.732

Here is a thread that explains the equations step by step -> http://testguy.net/threads/1341-Easy-way-to-calculate-transformer-fault-current

joaogemal
June 23, 2015, 11:29 AM
Here the information:
12,470-480Y/277V
1000kVA, 6.25% impedance

another way:

For a impedance of 6.25%, your necessary voltage will be 6.25% of 480 Volts = 30 Volts
What that means:
With secondary shorted, if you apply 30 Volts, you will have full transformer current, which is:
35 (remeber to multiply by 1000 (KVA to VA conversion)
I = 1202.85 A
from here you calculate your transformer Impedance
Z = V/I......Z = 30/1202.85.......Z = 0.025 Ohms.
Your max short-circuit current:
I = V/Z.......I = 480/0.025 = 19200 A

ryan.chapman@emerson.com
June 24, 2015, 09:55 PM
Thanks for the help.

rofo42
September 20, 2018, 08:50 AM
Here the information:
12,470-480Y/277V
1000kVA, 6.25% impedance

another way:

For a impedance of 6.25%, your necessary voltage will be 6.25% of 480 Volts = 30 Volts
What that means:
With secondary shorted, if you apply 30 Volts, you will have full transformer current, which is:
35 (remeber to multiply by 1000 (KVA to VA conversion)
I = 1202.85 A
from here you calculate your transformer Impedance
Z = V/I......Z = 30/1202.85.......Z = 0.025 Ohms.
Your max short-circuit current:
I = V/Z.......I = 480/0.025 = 19200 A
The link that Second Gen posted doesn't state anything about the additional steps you took dealing with the impedance.

Can anyone confirm?

joelcallow
September 24, 2018, 11:41 AM
Winding test results on a motor indicate possible degradation when the output waveforms show:
Winding waveform symmetry
Noticeable difference in winding waveforms
Chopped waveforms on grounded windings
Chopped waveforms on phase ungrounded windings

Having trouble getting an answer for this.