Log in

View Full Version : Purpose of Megger Guard Terminal



justin6354
June 23, 2015, 03:35 PM
What is the purpose of the Guard terminal on a Megohmeter?

SecondGen
June 23, 2015, 04:00 PM
When testing at higher voltages, such as with cable or transformers, the guard terminal can be used to divert surface leakage from the measuring circuit. For example, if you were performing a Primary to Ground test on a transformer you would guard the secondary windings. Not all insulation testers are equipped with a guard terminal.

36

joaogemal
June 24, 2015, 01:39 PM
If you understood that, which is a excellent explanation, you can transport to the Power Factor testing. The guard, for example, GST - Guard Red, is the same idea, divert from the measurement whatever is connected to the red.

wightywest
September 18, 2019, 04:01 PM
So does the guard allow voltages to pass through or does it immediately go to ground?

Relay1
September 19, 2019, 12:47 PM
So does the guard allow voltages to pass through or does it immediately go to ground?

A simple way to look at it is, you have a closed circuit with the current returning to it's source at the test equipment. Depending on how you hooked up the leads from the set, all or sections of the device current (Leakage) will be measured. The ground lead is just another path back to the test set whether you measure it or not.