View Full Version : Here's why you should always short a CT secondary



SecondGen
January 26, 2016, 10:27 AM
https://www.youtube.com/watch?v=j6v0ybdhGk0

Care must be taken that the secondary of a current transformer is not disconnected from its load while current is flowing in the primary, as the transformer secondary will attempt to continue driving current across the effectively infinite impedance up to its core saturation voltage.

This may produce a high voltage across the open secondary into the range of several kilovolts, causing arcing, compromising operator and equipment safety, or permanently affect the accuracy of the transformer.

codycody103
October 4, 2017, 01:29 PM
https://www.youtube.com/watch?v=j6v0ybdhGk0

Care must be taken that the secondary of a current transformer is not disconnected from its load while current is flowing in the primary, as the transformer secondary will attempt to continue driving current across the effectively infinite impedance up to its core saturation voltage.

This may produce a high voltage across the open secondary into the range of several kilovolts, causing arcing, compromising operator and equipment safety, or permanently affect the accuracy of the transformer.

Unless that ct is going to be put in service..., make sure those shorting screws are out prior to energizaton.

codycody103
October 4, 2017, 01:29 PM
Nice video btw

Vernon
October 4, 2017, 01:54 PM
Unless that ct is going to be put in service..., make sure those shorting screws are out prior to energizaton.

Wow! I have never tried that!

And you can verify the secondary circuit integrity with the secondary injection function of my CT test set.

See www.cttestset.com and read all about it.

ElectricalTestTech
October 4, 2017, 02:00 PM
Unless that ct is going to be put in service..., make sure those shorting screws are out prior to energizaton.

Cody,

Why do you mention "to remove shorting screws prior to energizing"? If you forget to remove them and energize the circuit, just remove them after energizing.

Unless your point was to make sure you don't defeat your protection devices, then you would want to make sure shorting screws are removed before you walk away for good.

lfmontoyas
October 7, 2017, 01:37 PM
Unless that ct is going to be put in service..., make sure those shorting screws are out prior to energizaton.

Excellent video. Thank you.

roberts311
May 20, 2018, 07:39 AM
https://www.youtube.com/watch?v=j6v0ybdhGk0

Care must be taken that the secondary of a current transformer is not disconnected from its load while current is flowing in the primary, as the transformer secondary will attempt to continue driving current across the effectively infinite impedance up to its core saturation voltage.

This may produce a high voltage across the open secondary into the range of several kilovolts, causing arcing, compromising operator and equipment safety, or permanently affect the accuracy of the transformer.

Good post. Nice video, too. I was interested to see how the axe was going to come into play.

ibeam01
August 17, 2020, 12:43 PM
This might be the most "hillbilly" safety video I've seen! haha

beeksYOW
January 31, 2021, 10:26 AM
I've always been told this but never had the visual, thanks for sharing!