PDA

View Full Version : Need GE Power+ TU Curves



SecondGen
March 2, 2016, 07:42 AM
Does anyone have trip curves for GE Power+ trip units? Only thing I can find online is generic curves from the users manual.

dnigra
March 2, 2016, 10:06 AM
http://www.electricalmanuals.net/manual-categories/low-voltage-equipment/breakers/ge/microversa-trip-unit/6752-des-001a

so im not too familiar with this trip unit, but this curve may also apply to the power plus?

Dan

SecondGen
March 2, 2016, 02:30 PM
This is perfect, you just saved the day! I have 6 of these to test. Thanks!

SecondGen
March 2, 2016, 02:32 PM
Also just an FYI - you can use the TVRMS-2 test kit to defeat ground fault on the Power+ for high current testing!

scottxclark
March 2, 2016, 03:48 PM
http://www.geindustrial.com/your-business/consulting-design-engineer/time-current-curves

dnigra
March 7, 2016, 07:11 AM
This is perfect, you just saved the day! I have 6 of these to test. Thanks!

NO PROBLEM!