View Full Version : watt-hour meter: finding revolutions per minute?
Bradfoxthelegend
July 6, 2016, 08:56 AM
This is the question from the test:
If a watt-hour meter has a disk constant of 3.6 is used with 600:5 ampere current transformers and 20:1 potential transformers, the primary Kh is?
The answers are in revolutions per minute. How do I get to revolutions per minute without knowing any of the output values?
Skyehaven40
July 19, 2017, 10:41 PM
This is the question from the test:
If a watt-hour meter has a disk constant of 3.6 is used with 600:5 ampere current transformers and 20:1 potential transformers, the primary Kh is?
The answers are in revolutions per minute. How do I get to revolutions per minute without knowing any of the output values?
=3.6*(600/5)*(20/1)
=8640
jflan13
January 18, 2018, 10:37 AM
=3.6*(600/5)*(20/1)
=8640
I have been looking for a way to answer that question for quite a bit. So simple and straight forward, Thank you
mcmahanrf
June 24, 2021, 08:09 AM
Simplify your current and voltage ratios:
Current 600:5 = 120:1
Voltage 20:1 = 20:1
Now assume a supply voltage and current, pick something that makes your math easy
Voltage:200V
Current:120A
Now calculate the watts for those current and voltage values for both sides of the instrument transformers:
Primary: 200V * 120A = 24,000 Watts*hr
Secondary: (200/20)V * (120/120)A = 10 Watts*hr
Now using your secondary disk constant that was given (3.6, this is the number of watt*hr per revolution of the disk) we can determine the number of turns per hr:
(10 watts*hr)/(3.6 watt*hr/turn) = 2.77777 turns (in one hour)
Now working backwards with that turn rate we can find the primary Kh:
(24,000 watts*hr)/(2.77777 turns) = 8640 watt*hr/turn or 8640 Kh
I have been looking for a way to answer that question for quite a bit. So simple and straight forward, Thank you
Powered by vBulletin® Version 4.2.5 Copyright © 2026 vBulletin Solutions Inc. All rights reserved.