View Full Version : Determine the approximate short circuit current available
rasilva
January 16, 2017, 07:25 PM
Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance
60,000 A
54,500 A
42,000 A
37,500 A
25,000 A
first should be 480Y/277 not 277y/480.
basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
z= (100/5)= 20
short circuit = 3007.08*20= 60189
so i would just go with the closest answer correct? and also they should fix the error on 277Y.
Flashman
January 16, 2017, 09:16 PM
I work it out to the same answer. Seems you did it right and I would go for the closest answer.
Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance
60,000 A
54,500 A
42,000 A
37,500 A
25,000 A
first should be 480Y/277 not 277y/480.
basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
z= (100/5)= 20
short circuit = 3007.08*20= 60189
so i would just go with the closest answer correct? and also they should fix the error on 277Y.
madMAX
January 17, 2017, 03:16 PM
The questions clearly states "determine the approximate short circuit current". Go with the closest answer.
rasilva
January 17, 2017, 03:19 PM
The questions clearly states "determine the approximate short circuit current". Go with the closest answer.
yes sir but its wrong wording that what confused 277y/480 doesn't exist, 480y/277 exist
Shaun103
April 27, 2017, 06:57 AM
Using the given information, determine the approximate short circuit current available at the transformer secondary: 13,800-277Y/480V, 2500 kVA, 5% Impedance
60,000 A
54,500 A
42,000 A
37,500 A
25,000 A
first should be 480Y/277 not 277y/480.
basically this would be the calculation. I= (2500*1000)/(480*1.732)= 3007.08
z= (100/5)= 20
short circuit = 3007.08*20= 60189
so i would just go with the closest answer correct? and also they should fix the error on 277Y.
2500 x 100
1.732 x .480 x5
250,000/4.1568= 60,142
Ronwilson1801
December 21, 2018, 06:25 PM
Could someone explain the math a little more in depth? Never mind I was confused in Z, but looking over it again I understand.
carl21
December 24, 2021, 05:21 PM
480 *1.732= 831.36
why do you multiply 480 by 1.732?
Kalbi_Rob
December 27, 2021, 06:17 AM
480 *1.732= 831.36
why do you multiply 480 by 1.732?
Original equation is for single phase transformer:
IFLA=(KVA*1000)/EL-L
To calculate for 3 phase voltage, the square root of 3 (1.732) must be multiplied by the voltage:
IFLA=(KVA*1000)/(EL-L*1.732)
EL-L for both of theses transformers is 480V, one is single phase and the other is 3 phase.