How do you figure out the distance required for a 3-point fall of potential test? I've heard you should drive your C2 anywhere from 3 to 10X the diagonal of the grid but I've seen other literature that give tables showing different values based on different distances.

To keep things simple, let's say we had a building that was 100' x 200', how far out would you take your leads?

184
This slide shows 10X diagonal.

183
This slide shows non-linear percentages.

Dnjob123
August 9, 2018, 03:20 PM
How do you figure out the distance required for a 3-point fall of potential test? I've heard you should drive your C2 anywhere from 3 to 10X the diagonal of the grid but I've seen other literature that give tables showing different values based on different distances.

To keep things simple, let's say we had a building that was 100' x 200', how far out would you take your leads?

184
This slide shows 10X diagonal.

183
This slide shows non-linear percentages.


Extract of IEEE Std 81.2-1991
it states to use 6.5 times the substation diagonal length/distance


267