Log in

View Full Version : What will each wattmeter indicate?



Stephen30002
July 21, 2017, 02:31 PM
Three coils with a resistance of 4 ohms and impedance of 13 ohms each are connected in wye to a 120/208 Volt panel. What will each wattmeter indicate if three single-phase wattmeters are used to measure the power?

The correct answer is 341W according to my answer sheet but I seem to keep getting 311W and I don't know what Im doing wrong. Any help would be great!

dennisrieves
September 14, 2017, 07:50 PM
Three coils with a resistance of 4 ohms and impedance of 13 ohms each are connected in wye to a 120/208 Volt panel. What will each wattmeter indicate if three single-phase wattmeters are used to measure the power?

The correct answer is 341W according to my answer sheet but I seem to keep getting 311W and I don't know what Im doing wrong. Any help would be great!

how did you come up with 311W? i'm having trouble with this question, not sure where to start.

baldscreen
October 6, 2017, 11:41 AM
Three coils with a resistance of 4 ohms and impedance of 13 ohms each are connected in wye to a 120/208 Volt panel. What will each wattmeter indicate if three single-phase wattmeters are used to measure the power?

The correct answer is 341W according to my answer sheet but I seem to keep getting 311W and I don't know what Im doing wrong. Any help would be great!

I get the same answer as you and verified it through calculator on this site: http://www.rapidtables.com/calc/electric/power-calculator.htm

Impedance Z = SQRT(4*4 + 13*13) = 8.823 Ohms
Angle Theta = ATAN (Impedance/Resistance) = ATAN (13/4) = 72.9 degrees
Total Power VA = V*V/Z = (120 * 120) / 8.823 = 1058.82 VA
Real Power Watts = Total Power * Cos Theta = 1058.82 * Cos(72.9) = 311 watts

Beats me how someone got 345 watts.

Allenxu
October 6, 2017, 02:19 PM
I get the same answer as you and verified it through calculator on this site: http://www.rapidtables.com/calc/electric/power-calculator.htm

Impedance Z = SQRT(4*4 + 13*13) = 8.823 Ohms
Angle Theta = ATAN (Impedance/Resistance) = ATAN (13/4) = 72.9 degrees
Total Power VA = V*V/Z = (120 * 120) / 8.823 = 1058.82 VA
Real Power Watts = Total Power * Cos Theta = 1058.82 * Cos(72.9) = 311 watts

Beats me how someone got 345 watts.

Impedance should be 13 ohms instead of 8.8

baldscreen
October 8, 2017, 12:36 PM
Impedance should be 13 ohms instead of 8.8

You are correct on the impedance. I was thinking of it as reactance ohms.

So, I'll try it again:

COS(Theta) = (Resistance/Impedance) = 4/13
225
Total Power VA = V*V/Z = (120 * 120) / 13 = 1107.69 VA
Real Power Watts = Total Power * Cos Theta = 1107.69*4/13 = 340.8 watts

Closer, but not quite the 345 watts given as the answer.

Lonpadams
November 6, 2018, 07:31 PM
PF = R/Z = 4/13 = 0.3077

E = I*R , 120 = I*13 , I = 120/13 = 9.23A

P = I*E , P = 9.23*120 = 1107.7VA

0.3077(PF) = W/1107.7VA , W = 1107.7*0.3077 = 340.84

340.84(W)/9.23A = 36.93V

36.93V/4OHMS = 9.23A

anthony
November 9, 2019, 10:02 AM
Three coils with a resistance of 4 ohms and impedance of 13 ohms each are connected in wye to a 120/208 Volt panel. What will each wattmeter indicate if three single-phase wattmeters are used to measure the power?

The correct answer is 341W according to my answer sheet but I seem to keep getting 311W and I don't know what Im doing wrong. Any help would be great!

120/13=9.230769231
watts is I(squared)times R.
9.230769231 (Sqaured) = 85.20710059
85.20710059 times 4 =340.8284024 watts

amarillo1970
January 6, 2021, 10:04 AM
Impedance should be 13 ohms instead of 8.8

I agree with you, in my calculator the result is 13.601 Ohms.