PDA

View Full Version : Witnessed an arc flash today on a 1200A distribution panel



SecondGen
November 7, 2017, 04:52 PM
I was doing an infrared scan for an electrical contractor on a 120V 1200A distribution board, and as they were closing up the front cover, one of the panel screws was drilled into a feeder cable that was sitting against the enclosure.


229


The resulting fault was pretty loud and there was a small fireball but thankfully nobody was hurt and everyone was wearing their PPE. The flash happened with the cover partially screwed on and the incident energy was somewhat contained.


230


Other than some burn marks and smoke damage inside the panel, everything was easily repairable. The cable and surrounding edges was wrapped with some rubber splicing tape around the flash site and everything was good to go.


231


Amazingly there was no service interruption, which was good because this distribution panel was feeding multiple emergency panels throughout a health care facility. The screw acted as a fuse and melted before the main upstream breaker could trip, you can see in the photo how long it was originally.


232


I wanted to share this story to serve as a reminder that things like this always happen when you least expect it. Stay safe out there.

ElectricalTestTech
November 8, 2017, 03:54 AM
Nice. That is one of my biggest fears with IR scanning. It’s not often that we get to scan new equipment. Most times it’s old equipment and the old panels are not the best to mess with. Over time we have seen panels evolve and become easier to open up while in service. But having a new panel isn’t justified if the craftsmanship isn’t the greatest. Craftsmanship can make a new panel even more dangerous to open than an old panel. Older panels could have 30+ years of ratty work done to them.

Just something to think about

jdptech
December 21, 2017, 11:10 PM
This is the second time I've heard of this happening...

jflan13
January 25, 2018, 08:20 PM
Nice. That is one of my biggest fears with IR scanning. It’s not often that we get to scan new equipment. Most times it’s old equipment and the old panels are not the best to mess with. Over time we have seen panels evolve and become easier to open up while in service. But having a new panel isn’t justified if the craftsmanship isn’t the greatest. Craftsmanship can make a new panel even more dangerous to open than an old panel. Older panels could have 30+ years of ratty work done to them.

Just something to think about

To tag onto that, the claw designs on a lot of the older Panels always keeps me on edge. Between them only grabbing half of the time and then when they do you have to worry about pinching wires. Almost gave an apprentice working with me and another guy a heart attack when a claw grabbed a circuit and blew it out right next to him.

SecondGen
January 25, 2018, 09:08 PM
To tag onto that, the claw designs on a lot of the older Panels always keeps me on edge. Between them only grabbing half of the time and then when they do you have to worry about pinching wires. Almost gave an apprentice working with me and another guy a heart attack when a claw grabbed a circuit and blew it out right next to him.

Yes, the older claw designs are ticking time bombs, especially the ones with no feet. I've seen circuits get blown many times.

It can't be stressed enough how mindful we must be when putting these older covers on and off. The very worst is when a wire gets pinched in a way that it blows when the next guy goes to take the cover off.

jflan13
January 27, 2018, 11:06 AM
Yes, the older claw designs are ticking time bombs, especially the ones with no feet. I've seen circuits get blown many times.

It can't be stressed enough how mindful we must be when putting these older covers on and off. The very worst is when a wire gets pinched in a way that it blows when the next guy goes to take the cover off.

The one site I have worked a for a couple of year started removing the claws, gluing the screws in place, and drilling new holes. It can be time consuming when you are trying to get it done the first time, but the next year I went back we got everything done in half the time.

SecondGen
January 27, 2018, 11:41 AM
The one site I have worked a for a couple of year started removing the claws, gluing the screws in place, and drilling new holes. It can be time consuming when you are trying to get it done the first time, but the next year I went back we got everything done in half the time.

Huge help, for sure. Another thing I've seen is drill/tap a hole top center and run a screw from the inside out, this gives you something to hang the cover on while you work the claws.

jflan13
January 27, 2018, 12:22 PM
Huge help, for sure. Another thing I've seen is drill/tap a hole top center and run a screw from the inside out, this gives you something to hang the cover on while you work the claws.

That would be extremely useful. I have seen guys do that on large panels without feet.

rofo42
April 21, 2018, 04:34 PM
Thank you for posting this. I recently started doing IR and needed the lesson in the "what if's". The company I work for has been offering to install IR port holes for later viewing when we have the panels off for circuit breaker testing etc. I'm not sure if many places are spending the money, but everytime I see a panel with these portholes, it makes you think how much safer it can make IR work.

roberts311
May 20, 2018, 07:28 AM
This post reminded me of the IR scans that I had been asked to do. Then I was alarmed on how many times I would do jobs like that or jobs like installing load monitoring equipment to live switchgear on my own. Things I would NEVER think about doing alone now. Jobs that if they asked me to do now and somewhat hinted that I would be doing it by myself...I would leave the company. If an incident had occurred at one of these sites, no one would know that something had happened unless maybe the lights went out and someone went to check the electrical room. Maybe later on in the evening my wife would call my manager and ask why I'm not answering my cell phone. This particular company PREACHED safety and then would send their technicians out alone to save some money and help their bottom line. The bottom line is that no company is worth a technicians life. Always try to have someone else with you.