Contact Timing test of VCB ( 11KV) was performed, timing results are as below :
Contact Timing Test:
Phase Closing Time Opening Time
L1 30.3 ms 22.3 ms
L2 30.5 ms 22.2 ms
L3 30.8 ms 22.2 ms
I need to know wheter or not these results are Okay? What is the limit ? Reference Standard??
bmclean
January 2, 2018, 09:49 PM
Best to look up the manufacture manual it should have open and close and close-open times in it as a general rule of thumb is <50ms for close is good <45ms for open is good and the close-open should be the combination of those two times.
jwdrowe
January 2, 2019, 08:36 PM
Contact Timing test of VCB ( 11KV) was performed, timing results are as below :
Contact Timing Test:
Phase Closing Time Opening Time
L1 30.3 ms 22.3 ms
L2 30.5 ms 22.2 ms
L3 30.8 ms 22.2 ms
I need to know wheter or not these results are Okay? What is the limit ? Reference Standard??
The manufacture manuals will tell you what the times should be, usually goes by cycles.