34. In accordance with NETA and IEEE standards the correct maintenance test voltage (dc) for 5KV rated EPR 133% insulation level cable is?
Your Answer: 14kV
Correct Answer: 11kV
Help: NETA-MTS 2015 TABLE 100.6.1
Is this correct as per NETA/ATS 2017. The way I am reading the standard it should be 36kV dc. Is this correct?.
Steviep
January 25, 2018, 09:26 AM
• Codes and Standards
34. In accordance with NETA and IEEE standards the correct maintenance test voltage (dc) for 5KV rated EPR 133% insulation level cable is?
Your Answer: 14kV
Correct Answer: 11kV
Help: NETA-MTS 2015 TABLE 100.6.1
Is this correct as per NETA/ATS 2017. The way I am reading the standard it should be 36kV dc. Is this correct?.
The question is looking to a maintenance voltage not acceptance.
lfmontoyas
January 25, 2018, 09:44 AM
The question is looking to a maintenance voltage not acceptance.
I am looking at NETA ATS-2017 table 100.6.1 and it says that for 5kV rated cable the maximum DC field Test Voltage During/After Installation for 133% Insulation Level is 36kV. I am trying to understand where the 11kV answer comes from. Any idea?.
Steviep
January 25, 2018, 09:58 AM
I am looking at NETA ATS-2017 table 100.6.1 and it says that for 5kV rated cable the maximum DC field Test Voltage During/After Installation for 133% Insulation Level is 36kV. I am trying to understand where the 11kV answer comes from. Any idea?.
You need to look at the NETA MTS table 100.6 which is the maintenance standards. The ATS is acceptance testing which will be a higher value to ensure reliability.
lfmontoyas
January 25, 2018, 10:06 AM
You need to look at the NETA MTS table 100.6 which is the maintenance standards. The ATS is acceptance testing which will be a higher value to ensure reliability.
Very Thankful. Are you memorizing all these values?. I am not sure what values to memorize?.
Steviep
January 25, 2018, 10:10 AM
Very Thankful. Are you memorizing all these values?. I am not sure what values to memorize?.
Im like a walking code book idk what it is but yea Ive got a lot of these number memorized even before i started studying for my NETA exams. I take my 3 on Monday. Best of luck!
SecondGen
January 25, 2018, 03:18 PM
Very Thankful. Are you memorizing all these values?. I am not sure what values to memorize?.
Here is the table from 2015 MTS...
234
Behab1
January 17, 2019, 01:21 PM
I am looking at NETA ATS-2017 table 100.6.1 and it says that for 5kV rated cable the maximum DC field Test Voltage During/After Installation for 133% Insulation Level is 36kV. I am trying to understand where the 11kV answer comes from. Any idea?.
The year matters.
chils15
January 31, 2019, 02:35 PM
Funny thing is in the field I never do dc for service age cable anymore, everything is vlf. It will still be on the test though.
test11
March 29, 2020, 11:45 AM
Funny thing is in the field I never do dc for service age cable anymore, everything is vlf. It will still be on the test though.
There are some hold-out customers that still use DC. Mainly city utilities where politics make it difficult to change the specs. That being said, some old site engineers aren't convinced either. I test DC a couple times a year for new cable.