Dave32
March 15, 2018, 09:43 PM
We are needing to do primary injecting testing on some Siemens WL breakers with an ETU745 & 766 trip unit. I have searched the internet and I can’t seem to find any curves for the units.

Also, I think to override the ground fault I need to jump pins 9 & 10 on 8X?

Any help would be appreciated.


Thanks
Dave.

SecondGen
March 16, 2018, 08:50 PM
We are needing to do primary injecting testing on some Siemens WL breakers with an ETU745 & 766 trip unit. I have searched the internet and I can’t seem to find any curves for the units.

Also, I think to override the ground fault I need to jump pins 9 & 10 on 8X?

Any help would be appreciated.


Thanks
Dave.

For that trip unit, I think you need to download the Siemens Time Current Curve (TCC) Software. Once installed, you can fill out the breaker info and trip unit settings and it will generate the curve for you.

http://w3.usa.siemens.com/powerdistribution/us/en/time-current-curve-software/pages/time-current-curve-software.aspx

You might find the software a bit difficult to use, its outdated and not designed very well. As for ground fault, if I remember correctly on that trip unit you need to change the ground fault sensing scheme to source ground when primary injection testing, this looks at current on the neutral sensor only.

I'm having trouble finding the specific manual for you trip unit. Some models have a switch, others have a jumper that can only be changed by removing the trip unit.

236

Kalbi_Rob
August 26, 2019, 11:55 AM
We are needing to do primary injecting testing on some Siemens WL breakers with an ETU745 & 766 trip unit. I have searched the internet and I can’t seem to find any curves for the units.

Also, I think to override the ground fault I need to jump pins 9 & 10 on 8X?

Any help would be appreciated.


Thanks
Dave.

This is the manual that answers your question, a little late, but good for anybody else:

https://docs.natlswgr.com/docs/W1000570.pdf

oarreola
August 26, 2019, 06:20 PM
What do you use to power up a ETU 776 trip unit out of the cubicle?

Kalbi_Rob
August 26, 2019, 06:46 PM
What do you use to power up a ETU 776 trip unit out of the cubicle?

If I remember right (its been years since I had to do this), you can supply 24Vdc to X8 terminals 3(+) and 4(-). That being said, you need to verify you have a true filtered dc power supply, or it can fry the ETU trip unit.

389

oarreola
August 26, 2019, 07:34 PM
If I remember right (its been years since I had to do this), you can supply 24Vdc to X8 terminals 3(+) and 4(-). That being said, you need to verify you have a true filtered dc power supply, or it can fry the ETU trip unit.

389

What would be the best way to filter the dc supply?

Kalbi_Rob
August 27, 2019, 07:14 AM
What would be the best way to filter the dc supply?

If your power supply has a DC regulator, it will have a pure DC output. If your using a power supply that uses a bridge rectifier with a capacitor, it could produce a ripple DC output. A ripple DC output can be used, but if the capacitor starts to fail, the ripple can become larger and damage sensitive DC equipment.

Thus, you need to know what kind of power supply you have based on manufacturer drawings. If you don't know, then your better off using the Siemens secondary kit, or powering up the switchboard CPT which powers up the equipment DC power supply.

SecondGen
August 27, 2019, 09:56 AM
What do you use to power up a ETU 776 trip unit out of the cubicle?

Siemens Secondary Kit, would recommend renting if you don't need it often.

oarreola
August 27, 2019, 10:16 AM
Thanks guys!

AaronCBI
August 27, 2019, 04:58 PM
I just performed primary injection testing on a WL type Siemens breaker with a ETU 745 trip unit.
The only way that I know of to obtain the time current curve is with their (Siemens) curve plotting software, Easy TCC.

AaronCBI
August 27, 2019, 05:02 PM
I know you got the terminal locations already, but just want to put in that Siemens is very particular about the 24 VDC that is applied to the trip unit. Iv tried using just a basic variable power supply and the trip unit did not power on. I had to obtain their test power supply which puts out a very steady 24 VDC (comparable to normal variable power supply). The representative I talk with told me it is something about wavelength filtering of the 24 VDC.

oarreola
August 28, 2019, 11:29 AM
I know you got the terminal locations already, but just want to put in that Siemens is very particular about the 24 VDC that is applied to the trip unit. Iv tried using just a basic variable power supply and the trip unit did not power on. I had to obtain their test power supply which puts out a very steady 24 VDC (comparable to normal variable power supply). The representative I talk with told me it is something about wavelength filtering of the 24 VDC.

Do you have a model number of that power supply, I’ve been trying to get a hold of a representative for a week now with no response.

Kalbi_Rob
August 29, 2019, 06:46 PM
I know you got the terminal locations already, but just want to put in that Siemens is very particular about the 24 VDC that is applied to the trip unit. Iv tried using just a basic variable power supply and the trip unit did not power on. I had to obtain their test power supply which puts out a very steady 24 VDC (comparable to normal variable power supply). The representative I talk with told me it is something about wavelength filtering of the 24 VDC.

Yes, that is what I was talking about with DC ripple voltage. Either you have to have a DC Voltage Regulator or a proper Capacitor to filter out the DC ripple to be a pure DC signal. Essentially, you are must completely remove the AC sine wave into a pure DC flat voltage.
Siemens electronics is very sensitive, and can be damaged if the ripple is too large.

AaronCBI
September 3, 2019, 03:38 PM
Do you have a model number of that power supply, I’ve been trying to get a hold of a representative for a week now with no response.

6EP1332-5BA20

oarreola
September 4, 2019, 11:29 AM
6EP1332-5BA20

Thanks

scottbouch
March 12, 2020, 02:28 PM
This is the manual that answers your question, a little late, but good for anybody else:

https://docs.natlswgr.com/docs/W1000570.pdf

To disable the ground fault during primary injection testing common 3 phases on the line side, then run current through 2 phases on the load side.

scottbouch
March 12, 2020, 02:31 PM
What do you use to power up a ETU 776 trip unit out of the cubicle?

look at the terminal block labeled x8 on the top of the breaker. The ETU 776 need 24v DC to power the trip unit.
On the x8 terminal block, hook the hot lead 24v to port #3. Hook the neutral lead to port #4

irishguy2010
September 24, 2020, 04:00 PM
To disable the ground fault during primary injection testing common 3 phases on the line side, then run current through 2 phases on the load side.

Install jumpers between contacts 9-10 to disable NGS
Install jumpers between contacts 11-12 to disable GFP