View Full Version : NETA 4 Exam Questions 7/2018
MartyCoyne
July 11, 2018, 07:18 AM
I took the NETA IV exam this Monday. There was maybe one or two questions from this entire site on the exam!!!
ejbrewer
July 11, 2018, 07:34 AM
I took the NETA IV exam this Monday. There was maybe one or two questions from this entire site on the exam!!!
How did it go? Do you have any info to share?
MartyCoyne
July 11, 2018, 08:57 AM
How did it go? Do you have any info to share?
I don't remember a lot of questions but I will post as they come back to me!!
MartyCoyne
July 11, 2018, 08:59 AM
I don't remember a lot of questions but I will post as they come back to me!!
1000kva 34.5kv to 480v secondary transformer 5% imp. apply 480v to primary side and short secondary to ground. What is primary fault current?
Lestracy31
July 11, 2018, 09:40 AM
1000kva 34.5kv to 480v secondary transformer 5% imp. apply 480v to primary side and ground secondary. What is primary fault current?
8.1A?
MartyCoyne
July 11, 2018, 10:56 AM
8.1A?
1000000/34500*1.732=16.73a
34500*.05=1725v
480 is to 1725 as X is to 16.73
480/1725=.2782 .2782*16.73=4.65a pri
Lestracy31
July 11, 2018, 11:18 AM
1000000/34500*1.732=16.73a
34500*.05=1725v
480 is to 1725 as X is to 16.73
480/1725=.2782 .2782*16.73=4.65a pri
thx forgot sqrt3 in my Ibase calculation
3Ashockers
July 12, 2018, 06:07 AM
1000kva 34.5kv to 480v secondary transformer 5% imp. apply 480v to primary side and ground secondary. What is primary fault current?
Assuming D-Y
Turns Ratio 34.5k to 277 = 124.5:1
Sec. phase voltage at 480 primary = 3.86V
Line Voltage from 480 primary = 6.68V
1,000,000VA / (1.732*6.7V) = 86.4kA
Secondary SC Current = 86.4/.05 = 1,729kA
Primary Current = 1,729,000 / 124.5 = 13.88kA SC
1electricalguru
July 23, 2018, 10:29 PM
I took the NETA IV exam this Monday. There was maybe one or two questions from this entire site on the exam!!!
The exams are all being rewritten to be more challenging as well as more fair in the information being tested. Ambiguous and "trick" questions (and the answer choices) are being eliminated. While I have not taken any of the practice questions on this site, I am going to assume that the questions are similar, not verbatim from previous exams. Obtaining a passing score on any of these NETA exams will require the ability to apply your industry knowledge and experience, not just rote memorization.
Wanderer20001us
December 26, 2018, 12:59 PM
Assuming D-Y
Turns Ratio 34.5k to 277 = 124.5:1
Sec. phase voltage at 480 primary = 3.86V
Line Voltage from 480 primary = 6.68V
1,000,000VA / (1.732*6.7V) = 86.4kA
Secondary SC Current = 86.4/.05 = 1,729kA
Primary Current = 1,729,000 / 124.5 = 13.88kA SC
Can someone explain to me how to differentiate between the wording of the test question and the two results other than looking at the magnitude of the answers? I have re-read the questions many times and cannot tell (other than answer choice) which method you would choose. They both appear to ask for the short circuit primary current, and short of the answers, I would get the answer of 4.65A as my answer. I mean, let's face it, if I hook up a 480 source to the primary with the secondary grounded, I'm going to get one or the other, not both.
Primepower1
January 7, 2019, 10:29 AM
I took the NETA IV exam this Monday. There was maybe one or two questions from this entire site on the exam!!!
This site is not for memorizing, it is to see questions that are similar to what would be on the test. It makes sense that the people that make the test questions would monitor this site and intentionally change numbers and wording, but still cover the same subjects.
MartyCoyne
January 7, 2019, 11:12 AM
This site is not for memorizing, it is to see questions that are similar to what would be on the test. It makes sense that the people that make the test questions would monitor this site and intentionally change numbers and wording, but still cover the same subjects.
young_dad
January 9, 2019, 12:46 PM
Can someone explain to me how to differentiate between the wording of the test question and the two results other than looking at the magnitude of the answers? I have re-read the questions many times and cannot tell (other than answer choice) which method you would choose. They both appear to ask for the short circuit primary current, and short of the answers, I would get the answer of 4.65A as my answer. I mean, let's face it, if I hook up a 480 source to the primary with the secondary grounded, I'm going to get one or the other, not both.
Check out this write up on calculating transformer SC currents. It is essentially an application of Ohm's law using the impedance of the transformer.
http://apps.geindustrial.com/publibrary/checkout/Short%20Circuit?TNR=White%20Papers|Short%20Circuit |generic
chils15
January 31, 2019, 02:29 PM
Check out this write up on calculating transformer SC currents. It is essentially an application of Ohm's law using the impedance of the transformer.
http://apps.geindustrial.com/publibrary/checkout/Short%20Circuit?TNR=White%20Papers|Short%20Circuit |generic
good read worth the time
bnhocking
January 31, 2019, 05:47 PM
1000kva 34.5kv to 480v secondary transformer 5% imp. apply 480v to primary side and short secondary to ground. What is primary fault current?
I have seen this question very similar in the level 4 test bank.
JesseJames
February 26, 2020, 08:36 PM
Can someone explain to me how to differentiate between the wording of the test question and the two results other than looking at the magnitude of the answers? I have re-read the questions many times and cannot tell (other than answer choice) which method you would choose. They both appear to ask for the short circuit primary current, and short of the answers, I would get the answer of 4.65A as my answer. I mean, let's face it, if I hook up a 480 source to the primary with the secondary grounded, I'm going to get one or the other, not both.
The question is what is the current in the primary winding when you put 480VAC across it....somehow the word "FAULT" got typed in there before "CURRENT"...
I think the 4.65A is correct.
test11
April 2, 2020, 07:14 PM
Assuming D-Y
Turns Ratio 34.5k to 277 = 124.5:1
Sec. phase voltage at 480 primary = 3.86V
Line Voltage from 480 primary = 6.68V
1,000,000VA / (1.732*6.7V) = 86.4kA
Secondary SC Current = 86.4/.05 = 1,729kA
Primary Current = 1,729,000 / 124.5 = 13.88kA SC
These answers are much higher than normal current in the transformer. This is impossible as the impedance of the transformer is unchanged and the voltage decreased significantly. Using ohms law, the current must be much lower than normal which is 16.73A. Therefore, the KVA of the transformer is different at this voltage and cannot be used directly as a basis in finding the current at the new lower voltage.
rdemarce
May 1, 2020, 08:03 PM
These answers are much higher than normal current in the transformer. This is impossible as the impedance of the transformer is unchanged and the voltage decreased significantly. Using ohms law, the current must be much lower than normal which is 16.73A. Therefore, the KVA of the transformer is different at this voltage and cannot be used directly as a basis in finding the current at the new lower voltage.
The KVA of the transformer is the same regardless of what voltage is on the transformer. As your voltage drops, your current goes up in order to achieve the same KVA rating. You all have to remember that transformers are rated in Power, not voltage or current by themselves. The transformer doesn't care what voltage is on the windings, it's going to provide the amount of power that it can supply - once you factor in the impedance of the transformer.
test11
May 2, 2020, 01:25 PM
The KVA of the transformer is the same regardless of what voltage is on the transformer. As your voltage drops, your current goes up in order to achieve the same KVA rating. You all have to remember that transformers are rated in Power, not voltage or current by themselves. The transformer doesn't care what voltage is on the windings, it's going to provide the amount of power that it can supply - once you factor in the impedance of the transformer.
No. Transformer impedance stays the same, but voltage is reduced. Therefore current goes down with voltage. As a matter of fact, you can look up how percent impedance is calculated. They just raise voltage on the primary with a shorted secondary winding and see what percentage of rated voltage it takes to produce the rated KVA.
In short, power draw is dependent on all of ohm's law. You have to look at it accordingly.
rdemarce
May 2, 2020, 02:41 PM
No. Transformer impedance stays the same, but voltage is reduced. Therefore current goes down with voltage. As a matter of fact, you can look up how percent impedance is calculated. They just raise voltage on the primary with a shorted secondary winding and see what percentage of rated voltage it takes to produce the rated KVA.
In short, power draw is dependent on all of ohm's law. You have to look at it accordingly.
I agree that power is dependent on ohm’s law and the transformer impedance stays the same. I 100% disagree with the rest of your post.
The available fault current is the same no matter what voltage is applied to the primary windings of the transformer. Assume an infinite bus supplying the transformer and a shirt to ground on the secondary. The short to ground will take all of the current the transformer can throw at it, therefore the current on the primary windings will be the same amount of current as there would be if the rated voltage was applied to the transformer.
Every time there is a ground fault, what happens? Using ohm’s law, power equals I(squared)*Resistance.
If the resistance approaches zero (we know it’s not actually zero) then current has to approach infinity.
In a transformer, power is your constant. Power is dependent on more than just “ohm’s law” because your statement implies power can only be calculated by volts and amps. But if you use current and resistance you see what actually happens.
To answer the question, you find the available fault current on the primary winding (at whatever voltage you want) and that is the answer no matter what voltage is used on the primary windings.
test11
May 3, 2020, 05:14 PM
I agree that power is dependent on ohm’s law and the transformer impedance stays the same. I 100% disagree with the rest of your post.
The available fault current is the same no matter what voltage is applied to the primary windings of the transformer. Assume an infinite bus supplying the transformer and a shirt to ground on the secondary. The short to ground will take all of the current the transformer can throw at it, therefore the current on the primary windings will be the same amount of current as there would be if the rated voltage was applied to the transformer.
Every time there is a ground fault, what happens? Using ohm’s law, power equals I(squared)*Resistance.
If the resistance approaches zero (we know it’s not actually zero) then current has to approach infinity.
In a transformer, power is your constant. Power is dependent on more than just “ohm’s law” because your statement implies power can only be calculated by volts and amps. But if you use current and resistance you see what actually happens.
To answer the question, you find the available fault current on the primary winding (at whatever voltage you want) and that is the answer no matter what voltage is used on the primary windings.
Ohm's law:451
Impedance, as you know, stays basically the same for the test as its simulated shorted to ground on the secondary side. Then, if you reduce the voltage, what has to happen to current? That is the current you plug into that power equation. So KVA is not constant.
The KVA max OUTPUT staying constant at a large primary voltage range above percent impedance voltage is due to saturation and is outside the original scope of the question. It requires higher math to look at as primary impedance actually does change in this scenario (See SCPT or magnetic amplifiers at your peril).
Again, at a tech level with one dependent, one independent, and one fixed variable, KVA will not be constant and power in will equal power out(unlike in saturation).
Kalbi_Rob
May 3, 2020, 11:47 PM
Ohm's law:451
Impedance, as you know, stays basically the same for the test as its simulated shorted to ground on the secondary side. Then, if you reduce the voltage, what has to happen to current? That is the current you plug into that power equation. So KVA is not constant.
The KVA max OUTPUT staying constant at a large primary voltage range above percent impedance voltage is due to saturation and is outside the original scope of the question. It requires higher math to look at as primary impedance actually does change in this scenario (See SCPT or magnetic amplifiers at your peril).
Again, at a tech level with one dependent, one independent, and one fixed variable, KVA will not be constant and power in will equal power out(unlike in saturation).
Just gonna put this here:
https://www.electricaleasy.com/2014/04/open-and-short-circuit-test-on-transformer.html
"The ammeter reading gives primary equivalent of full load current (Isc). The voltage applied for full load current is very small as compared to rated voltage. Hence, core loss due to small applied voltage can be neglected. Thus, the wattmeter reading can be taken as copper loss in the transformer."
EricGoetz92
February 25, 2021, 10:14 AM
Assuming D-Y
Turns Ratio 34.5k to 277 = 124.5:1
Sec. phase voltage at 480 primary = 3.86V
Line Voltage from 480 primary = 6.68V
1,000,000VA / (1.732*6.7V) = 86.4kA
Secondary SC Current = 86.4/.05 = 1,729kA
Primary Current = 1,729,000 / 124.5 = 13.88kA SC
This is not how you do this. The percent impedance is a percent of the base impedance, which is calculated by using the base VA and V ratings. So you cannot use the "divide the FLA by the percent impedance" shortcut if you aren't using the base voltage to calculate the FLA since the percent impedance is a percent of the base impedance. Plus, if you were to short out the low side and apply 34.5kV to the high side, your high side current would be 334.69 A, so how does it make any sense that you would have 40x that when you are applying 1% of that voltage across the same amount of impedance?
EricGoetz92
February 25, 2021, 10:26 AM
The KVA of the transformer is the same regardless of what voltage is on the transformer. As your voltage drops, your current goes up in order to achieve the same KVA rating. You all have to remember that transformers are rated in Power, not voltage or current by themselves. The transformer doesn't care what voltage is on the windings, it's going to provide the amount of power that it can supply - once you factor in the impedance of the transformer.
The KVA rating of a transformer is based on how much KVA it can handle at the voltages listed on the nameplate and is based on it's construction (winding conductor ampacity, cooling capabilities, etc.). And transformers don't dictate how much flows through them, that is all dependent on how much the load demands and the source can supply. Certain machines, like motors, will draw more current at lower voltages to maintain the same horsepower output, but you can't treat transformers this way. If you were to apply half as much voltage to the transformer, it would cut down the VA rating because the windings won't magically increase the conductor size and ampacity and be able to handle twice as much current without generating more heat.
young_dad
February 25, 2021, 10:26 AM
This is not how you do this. The percent impedance is a percent of the base impedance, which is calculated by using the base VA and V ratings. So you cannot use the "divide the FLA by the percent impedance" shortcut if you aren't using the base voltage to calculate the FLA since the percent impedance is a percent of the base impedance. Plus, if you were to short out the low side and apply 34.5kV to the high side, your high side current would be 334.69 A, so how does it make any sense that you would have 40x that when you are applying 1% of that voltage across the same amount of impedance?
If I recall correctly, you are correct and that was made clear in another post. I think maybe all the responses to this questions were collected somewhere else?
EricGoetz92
February 25, 2021, 11:26 AM
If I recall correctly, you are correct and that was made clear in another post. I think maybe all the responses to this questions were collected somewhere else?
If they were collected somewhere else, the TestGuy admins didn't see it because they still have a practice test question that doesn't have anywhere close to the right answer as a choice. And the "Help" for this question links to this thread, which shows a lot of incorrect information about how to do this problem.
None of this is your fault of course, this is just one of my huge gripes about this site. They create practice test questions without even knowing what they are talking about. I'll end up submitting this question to the thread that is about correcting inaccurate test questions.
Primepower1
February 25, 2021, 11:45 AM
This is not how you do this. The percent impedance is a percent of the base impedance, which is calculated by using the base VA and V ratings. So you cannot use the "divide the FLA by the percent impedance" shortcut if you aren't using the base voltage to calculate the FLA since the percent impedance is a percent of the base impedance. Plus, if you were to short out the low side and apply 34.5kV to the high side, your high side current would be 334.69 A, so how does it make any sense that you would have 40x that when you are applying 1% of that voltage across the same amount of impedance?
EricGoetz92,
If that calculation is not right, can you respond with the correct calculation? It seems to make sense to me, please show the correct answer, in a line by line formula format. I got a similar answer for the primary current short circuit at 34.5 KV to 277 V / 1MVA 5% impedance, 334.69 amps SC primary, and I multiplied it by the ratio of the difference between 34,500 and 480, 71.875, and I got 24,054.4 amps for a 480 volt primary, or would you divide the ratio to get 4.656 amps, this always confuses me.
young_dad
February 25, 2021, 11:57 AM
EricGoetz92,
If that calculation is not right, can you respond with the correct calculation? It seems to make sense to me, please show the correct answer, in a line by line formula format.
https://testguy.net/threads/6409-Transformer-Primary-Injection-Testing-Calculation
EricGoetz92
February 25, 2021, 12:27 PM
EricGoetz92,
If that calculation is not right, can you respond with the correct calculation? It seems to make sense to me, please show the correct answer, in a line by line formula format.
Here is the problem and solution:
1000kva D-Y 34.5kv to 480/277v secondary transformer 5% imp. Apply 480v to primary side and ground secondary. What is primary fault current?
Find primary side Full Load Amps (FLA) at nameplate voltage:
FLA = (VA nameplate)/(V nameplate*sqrt(3)) = 1000kVA/(34.5kV * sqrt(3)) = 16.734 A
(FYI, when calculating the FLA on a three phase transformer, the formula is always the same whether it is the delta or wye winding.)
Find the maximum short circuit current at rated voltage:
I short circuit at rated voltage = FLA/(Percent Impedance) = 16.734 A/.05 = 334.69 A
Find the short circuit current at the applied voltage:
I short circuit at applied voltage = (V applied/V nameplate)*(I short circuit at rated voltage) = (480/34,500)*334.69 = 4.66 A
In conclusion, the impedance of the transformer doesn't change based on the applied voltage, so the short circuit current reduces proportionally the applied voltage. So you need to first find the short circuit current at rated voltage since that is the only voltage level you can use the "I short circuit = FLA/Percent Impedance" formula at. Then you multiply that by the ratio of applied voltage to name plate voltage and you get your answer.
If they asked you to find the amount of current flowing out of the secondary winding, you would do every step the exact same except during the first step where you calculate FLA, you would use 480V as the nameplate voltage instead of 34.5kV. You then use that FLA value moving forward. I won't write out the steps to that, but the answer would be 334.69 A.
Vysakh9292
June 22, 2022, 10:46 PM
1000000/34500*1.732=16.73a
34500*.05=1725v
480 is to 1725 as X is to 16.73
480/1725=.2782 .2782*16.73=4.65a pri
Thanks for the answer