View Full Version : GE SR745 Protective Relay
ElectricalTestTech
October 11, 2018, 10:22 AM
I was wondering if anyone had any type of spreadsheet or formula on how to calculate the currents needed to operate different parts of a differential slope. I am looking to be able to type in a primary winding current, and have it calculate the amount of secondary current needed to trip on differential. I have contacted GE and they do not have anything and basically state that we should just trust the relay. I have had so many relays fail in the past year that I do not trust their relays.
.2*CT diff p/u
25% slope1
1*CT break
98% slope 2
16MVA, 1200:5 primary, 3000:5 secondary, 13.8kV-4.16kV, Dyn1
I have a spreadsheet that allows me to input Winding 1 test amps and Winding 2 test amps. Based off of those it will tell me if I will see a trip or no trip. But I want to know the specific calculated pick up instead of having to continuously change my current values in the spreadsheet to get an approximate pick up.
Thanks
Relay1
October 15, 2018, 01:45 PM
I was wondering if anyone had any type of spreadsheet or formula on how to calculate the currents needed to operate different parts of a differential slope. I am looking to be able to type in a primary winding current, and have it calculate the amount of secondary current needed to trip on differential. I have contacted GE and they do not have anything and basically state that we should just trust the relay. I have had so many relays fail in the past year that I do not trust their relays.
.2*CT diff p/u
25% slope1
1*CT break
98% slope 2
16MVA, 1200:5 primary, 3000:5 secondary, 13.8kV-4.16kV, Dyn1
I have a spreadsheet that allows me to input Winding 1 test amps and Winding 2 test amps. Based off of those it will tell me if I will see a trip or no trip. But I want to know the specific calculated pick up instead of having to continuously change my current values in the spreadsheet to get an approximate pick up.
Thanks
I sent a couple of spreadsheets to your e-mail address. Hope they help!
ElectricalTestTech
October 15, 2018, 03:20 PM
I sent a couple of spreadsheets to your e-mail address. Hope they help!
Thank you. I will check them out tomorrow. I am trying to figure out this algorithm. It makes me mad that GE can’t provide a tool that other manufacturers do. I’ll be back at it tomorrow morning
Thanks again
Reef Donkey
September 18, 2019, 08:59 AM
I sent a couple of spreadsheets to your e-mail address. Hope they help!
Would you mind sharing them with me as well. I've ran into this same issue.
Relay1
September 19, 2019, 12:22 PM
Would you mind sharing them with me as well. I've ran into this same issue.
Hello Reef Donkey,
Hopefully there is a SEL-387 spread sheet attached here that may help you.
Relay1
Powered by vBulletin® Version 4.2.5 Copyright © 2026 vBulletin Solutions Inc. All rights reserved.