View Full Version : Most common rated insulation for control wiring
E-DivMafia
October 29, 2018, 05:34 PM
Which is the most common rated insulation for control wiring?
RickYoungblood
October 30, 2018, 06:36 PM
Which is the most common rated insulation for control wiring?
It’s 600V. That’s the common insulation class for panel wire
SecondGen
October 31, 2018, 02:26 PM
Which is the most common rated insulation for control wiring?
When I hear control wiring I think switchgear, which is normally 600V rated SIS wire.
Ronwilson1801
December 21, 2018, 07:17 PM
It’s 600V. That’s the common insulation class for panel wire
Is there a table or something where these values can be looked up?
E-DivMafia
December 28, 2018, 02:54 AM
Is there a table or something where these values can be looked up?
I am not aware of one, but would be interested to know as well.
Wanderer20001us
December 28, 2018, 06:30 AM
I am not aware of one, but would be interested to know as well.
NEC Table 310.104(A) provides application and insulation ratings for 600V class wire.
NEC Table 310.15(B)(16) provides ampacities.
SIS (insulation rating 90C) is what I would first think to use in most switchgear control wiring applications, but it can vary based on actual need in a substation or switchgear.
SecondGen
December 28, 2018, 08:15 AM
I am not aware of one, but would be interested to know as well.
Here is a PDF with various tables from NEC Article 310, might be worth a look: https://www.houwire.com/pdf/Article_310-Conductors_for_General_Wiring.pdf
Powered by vBulletin® Version 4.2.5 Copyright © 2026 vBulletin Solutions Inc. All rights reserved.