View Full Version : What is the alternator phase current?
wayneups
January 17, 2019, 10:36 AM
A delta-connected three-phase alternator is driving a wye-connected resistive load. The alternator output voltage is 480 V. The load resistors are 12 ohms each. What is the phase current in the alternator?
Your Answer: 13.33 A
Correct Answer: 40 A
The correct answer is not correct.
kingRADi88
February 3, 2019, 12:14 AM
A delta-connected three-phase alternator is driving a wye-connected resistive load. The alternator output voltage is 480 V. The load resistors are 12 ohms each. What is the phase current in the alternator?
Your Answer: 13.33 A
Correct Answer: 40 A
The correct answer is not correct.
Agree with your assessment. My math:
Find phase voltage of Wye connected load => 480V/ sqrt(3) = 277.128 V
Find phase current of load => I = E/R = 277.128V / 12 ohm = 23.094 A
Find phase current of source => current of phase = current of line in wye connection => line current = 23.094A => current of phase in Delta = current of line / sqrt(3) = 23.094A / sqrt(3) = 13.33A
pallen
April 15, 2021, 08:21 PM
Agree with your assessment. My math:
Find phase voltage of Wye connected load => 480V/ sqrt(3) = 277.128 V
Find phase current of load => I = E/R = 277.128V / 12 ohm = 23.094 A
Find phase current of source => current of phase = current of line in wye connection => line current = 23.094A => current of phase in Delta = current of line / sqrt(3) = 23.094A / sqrt(3) = 13.33A
I calculated the same Amp values as above at first. Upon review i realized that the current calculation need to be done for the current circulating in the delta connected alternator and not the wye connected 3 phase load.
So no sqrt 3 conversion is necessary
add the 3 phase ohm values because they are all connected too the delta alternator.
12Ohms x 3= 36
480v line voltage divided by 36ohms = 13.33A is the phase current in the delta connected alternator.