PDA

View Full Version : Couple NETA III Questions



jaycee91
January 23, 2019, 11:00 AM
What is the expected Maximum Trip Time (in Seconds) for a 240V, 400A molded-case circuit breaker inverse time test at 300% of Rated Continuous Current?

230

275

300

350



1000kva 34.5kv to 480v secondary transformer 5% imp. Apply 480v to primary side and ground secondary. What is primary fault current?

8.1A

4.65A

5.72A

11.95A

Kalbi_Rob
January 23, 2019, 01:14 PM
What is the expected Maximum Trip Time (in Seconds) for a 240V, 400A molded-case circuit breaker inverse time test at 300% of Rated Continuous Current?

300
This is directly from NETA/ATS Table 100.7