A percentage differential relay with a 25 percent slope characteristic has 4.9 A in one restraint coil and 4.2A in the other. What is the calculated imbalance?

I have the answer from the help link of 16.6% but need help on the formulas used and calculation process.

Kalbi_Rob
April 30, 2019, 07:32 PM
A percentage differential relay with a 25 percent slope characteristic has 4.9 A in one restraint coil and 4.2A in the other. What is the calculated imbalance?

I have the answer from the help link of 16.6% but need help on the formulas used and calculation process.

First determine the difference between the restraint coils:
4.9A - 4.2A = 0.7A

Then calculate the % slope by using the smaller restraint coil current (can use either but the higher % slope is from the smaller restraint current):
0.7A / 4.2A = 0.166 * 100% = 16.6%.

16.6% < 25% so the relay will not operate.

jbren81
May 1, 2019, 08:28 PM
First determine the difference between the restraint coils:
4.9A - 4.2A = 0.7A

Then calculate the % slope by using the smaller restraint coil current (can use either but the higher % slope is from the smaller restraint current):
0.7A / 4.2A = 0.166 * 100% = 16.6%.

16.6% < 25% so the relay will not operate.

Thank you, I appreciate the help!

test11
April 6, 2020, 08:54 PM
First determine the difference between the restraint coils:
4.9A - 4.2A = 0.7A

Then calculate the % slope by using the smaller restraint coil current (can use either but the higher % slope is from the smaller restraint current):
0.7A / 4.2A = 0.166 * 100% = 16.6%.

16.6% < 25% so the relay will not operate.

Since it's percent differential, don't you use the biasing current to determine the slope %S=Id/Ib? Where Ib=(I1+I2)/2?