Hey all,
So I've been placed in the Relay team at work and have been at it for nearly 2 months. The most notable work experience so far has been terminating a Line panel w/ SEL-421 relays and the breaker it protects, a 34kV GE(from the 90's). I witnessed some End to End testing of said relays, hooked up some SCADA alarm wires etc.
Lately I've been helping with a Digital Fault Recorder system that monitors PT's and CT's inside the Utilities house at various substations. Interesting stuff.
I've bought "The Relay Testing Handbook" and am reading it to get more familiar with the different elements and how to test them. Also reading the Art and Science of Protective Relaying, although it's a little over my head right now.
I imagine I won't be set loose on any Relays in the field any time soon as I'm so new, but I figure at least I may try to understand whats going on while the other techs are commissioning/testing them.
Do you have any thoughts/links/books as to what I should be consuming to build a fundamental knowledge of Relay Protection? Note, (plant/industrial)electrician with 14 years experience just started in Utilities.
My study list so far:
CT's/PT's: ratios, connections,
Breakers: Understanding the control circuits, basic operations
Utility Substations: Identifying items on one line and field, power sources
Relays: Communicating to them, relay logic, settings, protection zones, protective elements
Any help would be appreciated. Thanks
Relay1
September 17, 2019, 06:57 AM
Hey all,
So I've been placed in the Relay team at work and have been at it for nearly 2 months. The most notable work experience so far has been terminating a Line panel w/ SEL-421 relays and the breaker it protects, a 34kV GE(from the 90's). I witnessed some End to End testing of said relays, hooked up some SCADA alarm wires etc.
Lately I've been helping with a Digital Fault Recorder system that monitors PT's and CT's inside the Utilities house at various substations. Interesting stuff.
I've bought "The Relay Testing Handbook" and am reading it to get more familiar with the different elements and how to test them. Also reading the Art and Science of Protective Relaying, although it's a little over my head right now.
I imagine I won't be set loose on any Relays in the field any time soon as I'm so new, but I figure at least I may try to understand whats going on while the other techs are commissioning/testing them.
Do you have any thoughts/links/books as to what I should be consuming to build a fundamental knowledge of Relay Protection? Note, (plant/industrial)electrician with 14 years experience just started in Utilities.
My study list so far:
CT's/PT's: ratios, connections,
Breakers: Understanding the control circuits, basic operations
Utility Substations: Identifying items on one line and field, power sources
Relays: Communicating to them, relay logic, settings, protection zones, protective elements
Any help would be appreciated. Thanks
Well "cotton;11001", you are in a pretty good spot for picking up info on relay and substation equipment. As you dig around in the "Explore TestGuy" links, videos and articles you can always find hidden gems and new directions to expand your knowledge base. Use the senior techs you work with for information and testing procedures. The one person I think who taught me the most was an apprentice that would not take "That's just how you do it!" as an answer. I had to stop and think about my actions and what info I was sharing with this person. Did I help them with this info or do they think I'm just blowing smoke. Never miss a chance to learn something new or share a learning opportunity.
wightywest
September 18, 2019, 04:07 PM
The relay testing handbook principles and practice author Chris Werstiuk is great! another one is the electric power equipment maintenance and testing book (I have the second edition maybe there is a third out by now) by Paul Gill. Good reads.
Kalbi_Rob
September 18, 2019, 07:51 PM
The relay testing handbook principles and practice author Chris Werstiuk is great! another one is the electric power equipment maintenance and testing book (I have the second edition maybe there is a third out by now) by Paul Gill. Good reads.
Chris Werstiuk also has a online training courses:
https://relaytraining.com/online-protective-relay-training-v3/
He also has a youtube channel:
https://www.youtube.com/user/ValenceETS/featured
I was lucky enough to see him give a seminar at Hands-on Relay School. It was interesting how he went from straight Calculus (nobody in the room had experience with Calculus) to basic vector math to explain 3-phase fault analysis. I learned more in that hour than any other course I've been through. I just wish I had his powerpoint slide to refresh my memory from time to time.
Gsharpes
September 21, 2019, 07:40 PM
Chris Werstiuk also has a online training courses:
https://relaytraining.com/online-protective-relay-training-v3/
He also has a youtube channel:
https://www.youtube.com/user/ValenceETS/featured
I was lucky enough to see him give a seminar at Hands-on Relay School. It was interesting how he went from straight Calculus (nobody in the room had experience with Calculus) to basic vector math to explain 3-phase fault analysis. I learned more in that hour than any other course I've been through. I just wish I had his powerpoint slide to refresh my memory from time to time.
Rob,
I have attached links to the two presentations that Chris has recently done at Hands on Relay School. I will also link to the archive for the past 7 years of HRS lectures. Not all of them are available but the committee has been trying to be better about making sure we have copies available on the website. Hope you are able to once again attend school in the future.
Thanks,
Greg
https://www.eiseverywhere.com/file_uploads/b861df4d03feb83f0dc23982ce1d73a0_HRS_End-End.pdf
https://www.eiseverywhere.com/file_uploads/1b859c9e3ffa064bfe2de78b83d380f0_TestingBreakerFai lureSchemes-ChrisWerstiuk.pdf
https://www.cm.wsu.edu/ehome/hrs/756931/
GreenHornet
September 25, 2019, 07:07 AM
the relay testing handbook is excellent and get on Chris's web site and follow his info and a good place to ask questions, i'll dig up some training and post it, GH
Hey all,
So I've been placed in the Relay team at work and have been at it for nearly 2 months. The most notable work experience so far has been terminating a Line panel w/ SEL-421 relays and the breaker it protects, a 34kV GE(from the 90's). I witnessed some End to End testing of said relays, hooked up some SCADA alarm wires etc.
Lately I've been helping with a Digital Fault Recorder system that monitors PT's and CT's inside the Utilities house at various substations. Interesting stuff.
I've bought "The Relay Testing Handbook" and am reading it to get more familiar with the different elements and how to test them. Also reading the Art and Science of Protective Relaying, although it's a little over my head right now.
I imagine I won't be set loose on any Relays in the field any time soon as I'm so new, but I figure at least I may try to understand whats going on while the other techs are commissioning/testing them.
Do you have any thoughts/links/books as to what I should be consuming to build a fundamental knowledge of Relay Protection? Note, (plant/industrial)electrician with 14 years experience just started in Utilities.
My study list so far:
CT's/PT's: ratios, connections,
Breakers: Understanding the control circuits, basic operations
Utility Substations: Identifying items on one line and field, power sources
Relays: Communicating to them, relay logic, settings, protection zones, protective elements
Any help would be appreciated. Thanks
SecondGen
September 28, 2019, 08:41 AM
Wow, what a great collection of resources in this thread! You have the substation fundamentals down, Art and Science of Protective Relaying would be my recommendation as well for relay theory. I'd recommend starting to play with old electromechanical relays if you can, also try and look up some old school user manuals on basic voltage and current relays. Hands-on is always going to be your best friend, see if you can get paired up with any of the relay guys at your shop. AVO offers some good basic relay classes too. Good luck!
cotton
September 29, 2019, 06:29 PM
Thank you all for the great suggestions. I went on a download spree of all the presentations from the Hands On Relay school and am working my way through the beginner themed stuff! Also, the youtube vids are a godsend. I've already got a litany of questions for the techs and leads at work. Here's to hoping I can meter them out slowly enough to not piss them off!
Cheers
cotton
September 29, 2019, 06:30 PM
the relay testing handbook is excellent and get on Chris's web site and follow his info and a good place to ask questions, i'll dig up some training and post it, GH
Yes I've bought those books and making my way through them! They are great.
Nick1234
January 12, 2020, 01:31 PM
Thanks for the resource list this has really helped with my relay knowledge.
thethomas56
January 21, 2020, 04:49 PM
Another vote for the The Relay Testing Handbook! It is a great resource. And whenever you can I would go to a Hands on Relay School at WSU in Pullman, WA. It is well worth the money even out of your own pocket.
Go Cougs!
GreenHornet
January 22, 2020, 10:23 AM
Hey all,
So I've been placed in the Relay team at work and have been at it for nearly 2 months. The most notable work experience so far has been terminating a Line panel w/ SEL-421 relays and the breaker it protects, a 34kV GE(from the 90's). I witnessed some End to End testing of said relays, hooked up some SCADA alarm wires etc.
Lately I've been helping with a Digital Fault Recorder system that monitors PT's and CT's inside the Utilities house at various substations. Interesting stuff.
I've bought "The Relay Testing Handbook" and am reading it to get more familiar with the different elements and how to test them. Also reading the Art and Science of Protective Relaying, although it's a little over my head right now.
I imagine I won't be set loose on any Relays in the field any time soon as I'm so new, but I figure at least I may try to understand whats going on while the other techs are commissioning/testing them.
Do you have any thoughts/links/books as to what I should be consuming to build a fundamental knowledge of Relay Protection? Note, (plant/industrial)electrician with 14 years experience just started in Utilities.
My study list so far:
CT's/PT's: ratios, connections,
Breakers: Understanding the control circuits, basic operations
Utility Substations: Identifying items on one line and field, power sources
Relays: Communicating to them, relay logic, settings, protection zones, protective elements
Any help would be appreciated. Thanks
See below resource list, many white papers and protective relay info available
Meter
Ametek www.ametekpower.com
Weschler www.weschler.com
Yokogawa www.yokogawa-usa.com
Relay
ABB - ASEA www.abb.com/AbbLibrary/DownloadCenter
Basler www.basler.com
Beckwith www.beckwithelectric.com
GE inactive products http://store.gedigitalenergy.com/Manuals
GE www.gedigitalenergy.com/multilin/manuals/index.htm
SEL www.selinc.com
Tyco (Agastat & Potter Brumfield) http://relays.tycoelectronics.com/pnb.asp
Test Equipment
Arbiter www.arbiter.com
AVO www.avotraining.com
Doble www.doble.com
Manta www.mantatest.com
Megger www.megger.com/us
Publications
The Relay Testing Handbook-A Practical Guide from the Field by Chris Werstiuk
Protective Relaying: Principles and Applications by J. Lewis Blackburn
Modern Solutions for Protection, Control, and Monitoring of Electric Power Systems by SEL
Journal of Reliable Power by SEL (Schweitzer Engineering Laboratories) www.selinc.com
Art & Science of Protective Relaying www.gedigitalenergy.com/multilin/notes/artsci/index.htm
elinks
www.relaytesting.net/
http://techtalk.relaytesting.net/
KungFuMonk
February 19, 2020, 07:26 PM
This a great list of free reading material. There a lot of sites that you can download material from. If in your area you have a Half Price Books, I have found many Power Engineering Books that can explain the basics here.
Good Luck!
Timotheus
April 7, 2020, 07:24 AM
Chris Werstiuk also has a online training courses:
https://relaytraining.com/online-protective-relay-training-v3/
He also has a youtube channel:
https://www.youtube.com/user/ValenceETS/featured
I was lucky enough to see him give a seminar at Hands-on Relay School. It was interesting how he went from straight Calculus (nobody in the room had experience with Calculus) to basic vector math to explain 3-phase fault analysis. I learned more in that hour than any other course I've been through. I just wish I had his powerpoint slide to refresh my memory from time to time.
I am new to the industry as well and this thread has all sorts of useful information from the members. Thank you everyone!
Kalbi_Rob
July 13, 2020, 07:44 AM
Rob,
I have attached links to the two presentations that Chris has recently done at Hands on Relay School. I will also link to the archive for the past 7 years of HRS lectures. Not all of them are available but the committee has been trying to be better about making sure we have copies available on the website. Hope you are able to once again attend school in the future.
Thanks,
Greg
https://www.eiseverywhere.com/file_uploads/b861df4d03feb83f0dc23982ce1d73a0_HRS_End-End.pdf
https://www.eiseverywhere.com/file_uploads/1b859c9e3ffa064bfe2de78b83d380f0_TestingBreakerFai lureSchemes-ChrisWerstiuk.pdf
https://www.cm.wsu.edu/ehome/hrs/756931/
I didn't take the advantage of downloading these lectures from the years previously, and now the link seems to be broken. Shame.
cotton
July 18, 2020, 11:12 AM
I didn't take the advantage of downloading these lectures from the years previously, and now the link seems to be broken. Shame.
I downloaded most of them Kalbi_Rob, if you like send me a dm and we can figure out how to share them. A lot of them are powerpoint presentations, so some of the slides are just to help the speaker. Still a lot of good info.
Gsharpes
April 15, 2021, 12:08 AM
I didn't take the advantage of downloading these lectures from the years previously, and now the link seems to be broken. Shame.
Sorry, it is disappointing that WSU deleted all the documents off their server. We are working on setting up a Hands on Relay School website that the committee will control. I believe we might have an archive of most of the old lectures that we will be able to post again when the site is complete.
Powered by vBulletin® Version 4.2.5 Copyright © 2026 vBulletin Solutions Inc. All rights reserved.