View Full Version : Complete the power triangle
jfoster
October 27, 2019, 06:41 PM
Complete the power triangle given 127.58 VAR and 150.11 VA
79.1 W, 58.2 PF
127.49 W, 31.79 PF
49.02 W, 31.79 PF
79.1 W, 49.02 PF
Mark For Later Review
I believe the correct answer should be 79.1 watts, 52.7 power factor.
Kalbi_Rob
October 30, 2019, 02:59 PM
Complete the power triangle given 127.58 VAR and 150.11 VA
79.1 W, 58.2 PF
127.49 W, 31.79 PF
49.02 W, 31.79 PF
79.1 W, 49.02 PF
Mark For Later Review
I believe the correct answer should be 79.1 watts, 52.7 power factor.
You might want to check your work for the power factor portion, but
I think they shouldn't call it PF but the angle since cos of theta is 0 - 1, not 58.2
answer I would select is 79.1 W, 58.2 PF
P=sqrt((150.11^(2))-(127.8^(2)))= 79.1 W
sin^(-1)(127.58/150.11) = 58.2 degrees
PF = cos(58.2) = 0.5269 = 0.53
testguy
November 2, 2019, 02:48 PM
You might want to check your work for the power factor portion, but
I think they shouldn't call it PF but the angle since cos of theta is 0 - 1, not 58.2
answer I would select is 79.1 W, 58.2 PF
P=sqrt((150.11^(2))-(127.8^(2)))= 79.1 W
sin^(-1)(127.58/150.11) = 58.2 degrees
PF = cos(58.2) = 0.5269 = 0.53
Question has been updated to reflect the angle rather than PF.