mmacdonell
January 18, 2020, 01:55 PM
I think yes. 100ft x .0025ohm/ft = 0.25ohm < .9ohm so its ok.
mmacdonell
January 18, 2020, 05:55 PM
11. A given CT is rated 600:5, C20, 0.3 B 0.9. Can this CT produce enough voltage to trip a relay (with near-zero burden) 50 feet away if connected to the relay with #14 awg (.0025 ohms/ ft) wire?
Not sure how to calculate this, can someone please help?
akumaleon
January 19, 2020, 04:41 PM
11. A given CT is rated 600:5, C20, 0.3 B 0.9. Can this CT produce enough voltage to trip a relay (with near-zero burden) 50 feet away if connected to the relay with #14 awg (.0025 ohms/ ft) wire?
Not sure how to calculate this, can someone please help?
So you have 0.0025 ohms/ft x 50 ft = 0.125 ohms of your total wire circuit.
5A from your CT (600:5) so you can produce: V=I*R= 5*0.125 = 0.625V
I believe that is the voltage you are looking for.
And your total burden in VA would just be 0.625V*5A= 3.125VA
mmacdonell
January 20, 2020, 08:07 PM
So you have 0.0025 ohms/ft x 50 ft = 0.125 ohms of your total wire circuit.
5A from your CT (600:5) so you can produce: V=I*R= 5*0.125 = 0.625V
I believe that is the voltage you are looking for.
And your total burden in VA would just be 0.625V*5A= 3.125VA
So no need to consider the accuracy, accuracy class or max burden?
akumaleon
January 22, 2020, 05:24 PM
So no need to consider the accuracy, accuracy class or max burden?
well I give you what the "circuit" values are. (the Z and voltage drop of your wire)
usually you will have the relay Z or VA to add to your wire... but in this case your relay burden is neglected.
A 0.3 B 0.9 rated metering-class CT means it will operate within 0.3 percent accuracy if the secondary burden does not exceed 0.9 ohms.
mmacdonell
January 23, 2020, 10:38 AM
well I give you what the "circuit" values are. (the Z and voltage drop of your wire)
usually you will have the relay Z or VA to add to your wire... but in this case your relay burden is neglected.
A 0.3 B 0.9 rated metering-class CT means it will operate within 0.3 percent accuracy if the secondary burden does not exceed 0.9 ohms.
Thank you. No need to consider the "C20" or "B" (CT Class)?
Also, the question was "will it produce enough voltage to trip the relay?
- If this is protection class, then the 0.9 means Volts @ 20x CT rating, NOT not to exceed 0.9 ohms
- How do we know how much voltage is required to trip the relay?
Cheers!
akumaleon
January 24, 2020, 09:03 AM
Thank you. No need to consider the "C20" or "B" (CT Class)?
Also, the question was "will it produce enough voltage to trip the relay?
- If this is protection class, then the 0.9 means Volts @ 20x CT rating, NOT not to exceed 0.9 ohms
- How do we know how much voltage is required to trip the relay?
Cheers!
-if this is a relaying CT (protection) ? saying C20 ... means '20' Maximum in Volts @ 20 times CT Amp Rating.
and with a CT ratio of 600:'5'. in that case it's V=I*R where if you need Ohms BURDEN you do R=V/I . Just like you said with 20x CT rating;
20V/ (5A*20) = 0.2 Ohms
for a C100 runing 5A with 20X --> it will be 1 Ohms
C200 --> 2 ohms
C400 --> 4 ohms
C50 --> 0.5 ohms
-To me it looks like your question (trick question) its a Metering CT and its based on how to calculate the total burden of your circuit.
I would have done the following;
0.0025 ohms/ft x 50 ft = 0.125 ohms one way of my wire so 2x = 0.25 ohms
neglect the relays Z etc...
The secondary voltage is my total resistance X CT rated amps = 0.25*5= 1.25 Volts
(on the first post I forgot to double the wire of the circuit sense you need 2 wires for close circuit)
mmacdonell
January 26, 2020, 03:49 PM
-if this is a relaying CT (protection) ? saying C20 ... means '20' Maximum in Volts @ 20 times CT Amp Rating.
and with a CT ratio of 600:'5'. in that case it's V=I*R where if you need Ohms BURDEN you do R=V/I . Just like you said with 20x CT rating;
20V/ (5A*20) = 0.2 Ohms
for a C100 runing 5A with 20X --> it will be 1 Ohms
C200 --> 2 ohms
C400 --> 4 ohms
C50 --> 0.5 ohms
-To me it looks like your question (trick question) its a Metering CT and its based on how to calculate the total burden of your circuit.
I would have done the following;
0.0025 ohms/ft x 50 ft = 0.125 ohms one way of my wire so 2x = 0.25 ohms
neglect the relays Z etc...
The secondary voltage is my total resistance X CT rated amps = 0.25*5= 1.25 Volts
(on the first post I forgot to double the wire of the circuit sense you need 2 wires for close circuit)
Thanks, I agree with you there but then ultimately the questions is do you have enough voltage to trip the relay. So how would we know the required voltage?
akumaleon
January 27, 2020, 10:50 PM
Thanks, I agree with you there but then ultimately the questions is do you have enough voltage to trip the relay. So how would we know the required voltage?
V= I * (Rs + Rb)
zslater
August 28, 2020, 09:02 PM
Thank you. No need to consider the "C20" or "B" (CT Class)?
Also, the question was "will it produce enough voltage to trip the relay?
- If this is protection class, then the 0.9 means Volts @ 20x CT rating, NOT not to exceed 0.9 ohms
- How do we know how much voltage is required to trip the relay?
Cheers!
You do have to consider the C20. That is the maximum voltage that the CT is able to produce. The circuit requires 25V in order to operate. Thus this CT will not work as a relaying CT. However, it will work as a metering CT because the total circuit burden is .25 which is less than the .9 burden rating the CT has.
I attached a link to a great powerpoint that has this exact question in it.
https://nanopdf.com/queue/instrument-transformer-basics_pdf?queue_id=-1&x=1598668221&z=MjA5LjE1MC4yNDAuMjE3
Hope this helps
Dublin
February 5, 2021, 10:28 AM
You do have to consider the C20. That is the maximum voltage that the CT is able to produce. The circuit requires 25V in order to operate. Thus this CT will not work as a relaying CT. However, it will work as a metering CT because the total circuit burden is .25 which is less than the .9 burden rating the CT has.
I attached a link to a great powerpoint that has this exact question in it.
https://nanopdf.com/queue/instrument-transformer-basics_pdf?queue_id=-1&x=1598668221&z=MjA5LjE1MC4yNDAuMjE3
Hope this helps
How do you know that it requires 25V in order to operate the circuit?
This would most likely be able to operate the relay. Most protection is set far below the 20xIn rule of thumb if the question was "Is this CT correctly sized to be used as a protection CT?" I would agree that it is not, but the question was would this operate the protection, and there is not enough information to answer that,
In all likelihood, it would operate the protection unless the protection is exclusively very high current trips such as an instantaneous trip.
To know if this would operate the relay, we would need to know the protection setpoints of the relay.