Log in

View Full Version : Load testing a newly installed battery bank, ANSI requirement?



Sanjayo
June 9, 2017, 02:50 PM
29. According to ANSI a newly installed battery bank should be load tested after:
a. 1 year
b. 2 years
c. 4 years
d. 5 years


Does anyone know the answer to this, I think its within 2 years of installation?

tallyson71
June 12, 2017, 10:36 AM
Does anyone know the answer to this, I think its within 2 years of installation?

Found this on one manufacturers documentation:

"Conduct load test two years[emphasis added] after installation and then every five years. When the
system’s capacity falls below 90% load test annually."

http://www.sbsbattery.com/PDFs/Battery-testing-schedule-IEEE-NERC.pdf

Sanjayo
June 12, 2017, 05:06 PM
Found this on one manufacturers documentation:

"Conduct load test two years[emphasis added] after installation and then every five years. When the
system’s capacity falls below 90% load test annually."

http://www.sbsbattery.com/PDFs/Battery-testing-schedule-IEEE-NERC.pdf

Good chart for reference, thank you for posting.