View Full Version : Doble Testing a Bushing: C2 reading higher than nameplate



Bob_Woodward
March 4, 2020, 11:48 AM
Does anyone have an explanation for high C2 readings when Doble testing transformer bushings?

The test was on a three winding transformer. All C2 values were consistent but approximately 40 pf higher than the nameplate value

SecondGen
March 4, 2020, 04:37 PM
Does anyone have an explanation for high C2 readings when Doble testing transformer bushings?

The test was on a three winding transformer. All C2 values were consistent but approximately 40 pf higher than the nameplate value

434

Increased capacitance could be short circuit in the layers. Attached is from Doble Test Procedures, section 3-25.

Bob_Woodward
March 4, 2020, 05:00 PM
434

Increased capacitance could be short circuit in the layers. Attached is from Doble Test Procedures, section 3-25.

Thanks for your reply, although this can occasionally be the case seeing this result consistently across 8 different bushings suggests to me that there is either an issue with the test procedure or another external factor influencing the results. It would be highly unusual for all bushings to experience a short.

Can you speak to any other possible explanations?

Thanks!

SecondGen
March 4, 2020, 05:14 PM
Thanks for your reply, although this can occasionally be the case seeing this result consistently across 8 different bushings suggests to me that there is either an issue with the test procedure or another external factor influencing the results. It would be highly unusual for all bushings to experience a short.

Can you speak to any other possible explanations?

Thanks!

If you are experiencing that many failures then I would say investigate the test procedure. Often times its very difficult to get a good connection on the C2 tap if you don't have the proper accessories. Its very easy to short to ground. I'd recommend using a small alligator clip jumper from the C2 spring to the HV hook. A rubber blanket can be used for insulation.

rofo42
March 5, 2020, 06:03 PM
Does anyone have an explanation for high C2 readings when Doble testing transformer bushings?

The test was on a three winding transformer. All C2 values were consistent but approximately 40 pf higher than the nameplate value
The name plate refers to the factory testing. It is my understanding that this value will always be lower than installed values.

The fact that they are all consistent tells me that you are seeing the difference between installed and not installed values.

Just a thought/guess.

jblunt92482
March 10, 2020, 09:06 PM
Dirty glass can have an effect on your power factor readings. If the insulators are porcelain or glass, then make sure they are clean before testing.

Without pictures, numbers, or data, it's hard to really go into further details on this. I know that the Doble lid works good for keeping the HV hook off of the transformer if you have it up there.

Also, I don't know if you are using FRANK or not, but I know that I've had issues with it with CCVT testing. Just because it tells you to investigate doesn't necessarily mean anything is wrong.

My 2 cents anyways.

Realtime
March 11, 2020, 10:47 AM
I think I ran into something similar many years ago. The bushings were ABB Type GOH on the LV side of a GSU. The HV side were probably O+C and tested fine. This was commissioning on a new unit, so I only had the nameplate data to go from. ABB was contacted and I got some kind of explanation that the factory tests are in an oil immersed stand, while my test had the LV winding of the GSU connected. Basically the gist of the letter was don't worry, its fine. I submitted that letter with my final report.

Bob_Woodward
March 15, 2020, 08:51 PM
If you are experiencing that many failures then I would say investigate the test procedure. Often times its very difficult to get a good connection on the C2 tap if you don't have the proper accessories. Its very easy to short to ground. I'd recommend using a small alligator clip jumper from the C2 spring to the HV hook. A rubber blanket can be used for insulation.

Thanks for your suggestion! I used a rubber blanket and was able to improve my test results

amlawren
April 2, 2020, 11:49 AM
Does anyone have an explanation for high C2 readings when Doble testing transformer bushings?

The test was on a three winding transformer. All C2 values were consistent but approximately 40 pf higher than the nameplate value

I assume the bushings are rated <69kV. People tend to forget that bushings in this class don't have set C2 capacitance & that your measurement can be different from nameplate when installed in an apparatus, compared to testing in air.

If your capacitance values were consistent across all three, then that will be the baseline for future maintenance tests. If future tests measure 10% off from the original benchmark value, there is a cause for concern. In that case, hopefully the technician behind you didn't add an extra ground connection to the flange, attempting to make the measurements closer to nameplate and throwing the real capacitance measurement off.

Meggerman
November 17, 2021, 08:37 AM
Hello Bob, you are not alone in experiencing the inconsistent readings for C2 across various bushings. I attended a presentation from ABB at a conference in New Brunswick Canada in 2019 - specifically on C2 testing, construction and value of the C2 test. In the presentation, David M Geibbel - Technical Director ABB Alamo TN presented evidence and statistical data showing that C2 was not a reliable indicator of health of a bushing - in other words, would one "condemn/change" a bushing based on the C2 result. David clearly indicated the answer to be NO. As well, when we asked ABB Bushing Headquarters in Sweden for a statement on C2 testing, they formally wrote back to state that C2 is not considered in failing or passing a bushing.
C2 testing is subject to many influences which are not seen in the C1 testing. Comparison to nameplate PF is contentious leaving only capacitance as a comparison. Trending, although useful in C1 testing is both difficult to keep up (as my experience, most users do not maintain the needed trending history)
In my opinion, C1 testing is your best determinent for health, and one MUST compare to nameplate PF and temperature correction is mandatory if at any extreme temperatures above 25C or below 15C.
There are new methods of testing bushings where the bushings are tested at both 60Hz PF and at lower frequency - down to 1 Hz PF with clear evidence of detecting issues very early in the degradation stages of the bushing - and one can compare the other phase results to determine if one specific bushing is changing.
Hope this is useful to you.

MuniGuy
March 9, 2022, 10:19 PM
Does anyone have an explanation for high C2 readings when Doble testing transformer bushings?

The test was on a three winding transformer. All C2 values were consistent but approximately 40 pf higher than the nameplate value

Are you shorting the bushings together of each winding? This is necessary. Readings can be higher if they are not.
I have seen C2 readings increase bc the xfmr itself was overheating. This caused the C2 to to increase on all 3 primary bushings. Remember,a change in capacitance indicates a physical change.

rofo42
March 10, 2022, 04:44 PM
Does anyone have an explanation for high C2 readings when Doble testing transformer bushings?

The test was on a three winding transformer. All C2 values were consistent but approximately 40 pf higher than the nameplate value

Since responding to this thread initially, I have tested 100+ bushings; both installed and not installed.

I can now confirm that what you are seeing is simply the addition of the transformer tank and oil being introduced into the equation.

It is completely normal and to be expected. Also, Doble explicitly states to not use rubber insulating mats to influence readings. Doing so only proves that you have an issue that you are masking; whether that issue is actual or as in this case, by design.

The PF should not deviate too much from nameplate values for C2, installed or not. The capacitance is what should be expected to change. Any amount of moisture inside the C2 will greatly affect the readings.

drobinson
July 21, 2022, 04:45 PM
Hello Bob, you are not alone in experiencing the inconsistent readings for C2 across various bushings. I attended a presentation from ABB at a conference in New Brunswick Canada in 2019 - specifically on C2 testing, construction and value of the C2 test. In the presentation, David M Geibbel - Technical Director ABB Alamo TN presented evidence and statistical data showing that C2 was not a reliable indicator of health of a bushing - in other words, would one "condemn/change" a bushing based on the C2 result. David clearly indicated the answer to be NO. As well, when we asked ABB Bushing Headquarters in Sweden for a statement on C2 testing, they formally wrote back to state that C2 is not considered in failing or passing a bushing.
C2 testing is subject to many influences which are not seen in the C1 testing. Comparison to nameplate PF is contentious leaving only capacitance as a comparison. Trending, although useful in C1 testing is both difficult to keep up (as my experience, most users do not maintain the needed trending history)
In my opinion, C1 testing is your best determinent for health, and one MUST compare to nameplate PF and temperature correction is mandatory if at any extreme temperatures above 25C or below 15C.
There are new methods of testing bushings where the bushings are tested at both 60Hz PF and at lower frequency - down to 1 Hz PF with clear evidence of detecting issues very early in the degradation stages of the bushing - and one can compare the other phase results to determine if one specific bushing is changing.
Hope this is useful to you.

Do you have any links or any documentation? I am getting dragged over the coals for not failing a transformer on bad C2. It is 13.8kV and the bushings had scaffolding surrounding them during the test. any links you could offer would be greatly appreciated! Thanks!