View Full Version : Power Transformers VS. Distribution Transformers
RedBrick
March 16, 2020, 08:33 PM
How do you define a power transformer and a distribution transformer? I have asked the question to a few people and haven't received an answer that is rooted in anything, but more or less an opinion. The closest thing I have found is in IEEE 141. 10.4.1.1 states "The distribution type covers the range of 3 to 500KVA; the power type covers all ratings above 500KVA."
NETA 2019 MTS 7.2.1.2.D.3 (Power-Factor Tests)
C-HL POWER Transformers: 2.0% or less
C-HL DISTRIBUTION Transformers: 5.0% or less
NETA TABLE 100.3 also differentiates between Power & Distribution Transformers
SecondGen
March 18, 2020, 04:56 PM
How do you define a power transformer and a distribution transformer? I have asked the question to a few people and haven't received an answer that is rooted in anything, but more or less an opinion. The closest thing I have found is in IEEE 141. 10.4.1.1 states "The distribution type covers the range of 3 to 500KVA; the power type covers all ratings above 500KVA."
NETA 2019 MTS 7.2.1.2.D.3 (Power-Factor Tests)
C-HL POWER Transformers: 2.0% or less
C-HL DISTRIBUTION Transformers: 5.0% or less
NETA TABLE 100.3 also differentiates between Power & Distribution Transformers
Far as I know, you are correct. Power transformers are those generally contained within substations (outdoor and indoor), where as distribution transformers are generally those used to "distribute" power throughout a facility or more specifically, the end user. 500kVA is generally the threshold, you will find NETA has different criteria for transformers based on the 500kVA rating.
RedBrick
March 18, 2020, 08:06 PM
Far as I know, you are correct. Power transformers are those generally contained within substations (outdoor and indoor), where as distribution transformers are generally those used to "distribute" power throughout a facility or more specifically, the end user. 500kVA is generally the threshold, you will find NETA has different criteria for transformers based on the 500kVA rating.
SecondGen thanks for the reply, appreciate it. The way NETA words it is a little confusing.
7.2.1.1 Dry Type low-voltage transformers, Small
NOTE: "This category consists of power transformers with windings rated 600 volts or less and sizes equal to or less than 167kVA single phase or 500kVa three-phase"
7.2.1.2 Dry Type transformers, Large
NOTE: "This category consists of power transformers with windings rated higher than 600 volts and low voltage transformers larger than 167 kVA single-phase or 500 kVA three-phase"
Powered by vBulletin® Version 4.2.5 Copyright © 2025 vBulletin Solutions Inc. All rights reserved.