I need Standard operation Procedure (SOP) of partial discharge test and Tan delta test

Kalbi_Rob
May 6, 2020, 05:05 PM
I need Standard operation Procedure (SOP) of partial discharge test and Tan delta test

IEEE Std 400.2™-2013 Guide for Field Testing of Shielded Power Cable Systems Using VLF

Specifically Section:
5.4 Tangent delta/differential tangent delta/tangent delta stability/leakage current/
harmonic loss current tests with VLF sinusoidal waveform

IEEE Std 400.3™-2006 IEEE Guide for Partial Discharge Testing of Shielded Power Cable Systems in a Field Environment

You can also contact a representative with the company for the test equipment you are using, as they typically will provide simplified procedures of the IEEE Std regulating the test.