What is the turns ratio for a delta wye 138000/12470 XFMR. What is the proper formula? Thanks
Kalbi_Rob
August 31, 2020, 05:43 AM
What is the turns ratio for a delta wye 138000/12470 XFMR. What is the proper formula? Thanks
First step is to only use phase to ground voltages.
For Delta, Line-to-Line = Phase-to-Ground voltages.
For Wye, SQRT(3) * Line-to-Line = Phase-to-Ground voltages. Vp=12470/SQRT(3)=12470/1.732=7199.8V
TTR=138000V/7200V=~19.166
Math should be correct minus rounding errors.
southbury
September 5, 2020, 07:20 PM
as the previous post already explained
These questions are hard to answer.
Even NETA is vague on the exams.
Given 138,000 to 12470
They do not tell you the connections( I protested these questions)
138,000 probably a line to line voltage so you would assume a delta
12470 probably a wye voltage. 12470/square root 3=7199.56=7200
138,000/7200=19.1666