View Full Version : Percentage Differential Mismatch
Uguessus
October 8, 2020, 04:39 PM
Calculate the percentage differential mismatch for an electromechanical relay protecting a 138kV-69kV Delta-Wye 50MVA Transformer with 250:5 CTs on the primary and 500:5 CTs on the secondary, with CT ratio taps on the relay set to 5A on the high side and 9A on the low side.
I need help with this problem, the answer is supposedly 3.78%. Thanks.
Erased
October 17, 2020, 08:22 AM
Calculate the percentage differential mismatch for an electromechanical relay protecting a 138kV-69kV Delta-Wye 50MVA Transformer with 250:5 CTs on the primary and 500:5 CTs on the secondary, with CT ratio taps on the relay set to 5A on the high side and 9A on the low side.
I need help with this problem, the answer is supposedly 3.78%. Thanks.
Now, I got a slightly different answer, so someone correct me if I'm mistaken.
First calculate HV currents.
Primary:
50000000/sqrt(3)*138000 = 209.18
Secondary:
50000000/sqrt(3)*69000 = 418.37
Now calculate CT currents. An electromechanical scheme on a Delta-Wye will have Wye-Delta CT's to account for the phase shift. Delta CT current must be multiplied by sqrt(3).
Primary - Wye CT:
209.18/50 = 4.18
Secondary - Delta CT:
418.37/100 = 4.18
4.18*sqrt(3) = 7.24
Calculate the percent mismatch as follows: On two-winding transformers,
determine the ratio of the two relay currents and the tap values selected. The
difference between these ratios, divided by the smaller ratio, is the percent
mismatch.
((4.18/5)-(7.24/9)) / (7.24/9) = 0.0392
3.92% with rounding errors.
Looks like your answer came from incorrectly dividing by the larger ratio.
(4.18/5)-(7.24/9) / (4.18/5) = 0.0377
3.77% with rounding errors.
Uguessus
October 17, 2020, 10:54 AM
This is awesome! Thanks a lot, Erased.
rjhrick03
February 7, 2021, 01:28 PM
If the below explanation is correct, the practice test question is still incorrect as of Feb 2021. Just want to confirm...the correct answer is 3.92%?
Now, I got a slightly different answer, so someone correct me if I'm mistaken.
First calculate HV currents.
Primary:
50000000/sqrt(3)*138000 = 209.18
Secondary:
50000000/sqrt(3)*69000 = 418.37
Now calculate CT currents. An electromechanical scheme on a Delta-Wye will have Wye-Delta CT's to account for the phase shift. Delta CT current must be multiplied by sqrt(3).
Primary - Wye CT:
209.18/50 = 4.18
Secondary - Delta CT:
418.37/100 = 4.18
4.18*sqrt(3) = 7.24
Calculate the percent mismatch as follows: On two-winding transformers,
determine the ratio of the two relay currents and the tap values selected. The
difference between these ratios, divided by the smaller ratio, is the percent
mismatch.
((4.18/5)-(7.24/9)) / (7.24/9) = 0.0392
3.92% with rounding errors.
Looks like your answer came from incorrectly dividing by the larger ratio.
(4.18/5)-(7.24/9) / (4.18/5) = 0.0377
3.77% with rounding errors.
khanhamza
February 8, 2021, 04:35 AM
https://cms-cdn.selinc.com/assets/Literature/Publications/Technical%20Papers/6451_PercentageRestrained_MT_20140319_Web.pdf?v=20 190509-181852
All information here related to the topic kindly visit this site and my collection its very helpful to you.Thank You!