View Full Version : Ground defeat digitrip 1150+ on Mag Ds
will_lunsford
December 5, 2020, 09:53 PM
what am I missing here. Can't find a defeat in any of the manuals. Secondaries don't have a ground defeat function for primary injection, I have what I thought was a ground defeat plug for the the secondary contacts with a jumper in but thats not working. I think it must just be the one for zone interlocking. I feel like I have figured this out before its just been years since i did primary on this one. Any help is much appreciated. Testing eaton magnum DS breakers with digitrip 1150+ trip units.
Kalbi_Rob
December 6, 2020, 04:22 PM
what am I missing here. Can't find a defeat in any of the manuals. Secondaries don't have a ground defeat function for primary injection, I have what I thought was a ground defeat plug for the the secondary contacts with a jumper in but thats not working. I think it must just be the one for zone interlocking. I feel like I have figured this out before its just been years since i did primary on this one. Any help is much appreciated. Testing eaton magnum DS breakers with digitrip 1150+ trip units.
Ground Fault is defeated by shorting terminal B6-B7
Zone Interlock is defeated by shorting terminal B8-B9
I do not remember if it is easily seen which terminal is which, but can be difficult determining which secondary terminal is A and which is B and whether it is read from inside or outside.
487
JohnRaz
December 6, 2020, 05:42 PM
what am I missing here. Can't find a defeat in any of the manuals. Secondaries don't have a ground defeat function for primary injection, I have what I thought was a ground defeat plug for the the secondary contacts with a jumper in but thats not working. I think it must just be the one for zone interlocking. I feel like I have figured this out before its just been years since i did primary on this one. Any help is much appreciated. Testing eaton magnum DS breakers with digitrip 1150+ trip units.
B-6 to B-7
488
will_lunsford
December 6, 2020, 07:12 PM
what am I missing here. Can't find a defeat in any of the manuals. Secondaries don't have a ground defeat function for primary injection, I have what I thought was a ground defeat plug for the the secondary contacts with a jumper in but thats not working. I think it must just be the one for zone interlocking. I feel like I have figured this out before its just been years since i did primary on this one. Any help is much appreciated. Testing eaton magnum DS breakers with digitrip 1150+ trip units.
Thank you all for your help.
Powered by vBulletin® Version 4.2.5 Copyright © 2026 vBulletin Solutions Inc. All rights reserved.