Log in

View Full Version : Applying a solidly grounded wire after hipot test



epenland
February 11, 2021, 08:08 PM
Applying a solidly grounded wire immediately after performing a high-potential test:

akumaleon
February 13, 2021, 02:43 PM
Applying a solidly grounded wire immediately after performing a high-potential test:

Will ensure immediate personally safety.
Requires a rubber glove.
May damage the test set.
May damage the insulation under test.
Is not necessary

darinlamos
February 19, 2021, 01:49 PM
Will ensure immediate personally safety.
Requires a rubber glove.
May damage the test set.
May damage the insulation under test.
Is not necessary

I saw this question and answered "Will ensure immediate personally safety." I didn't see it show up in my wrong answers.

khanhamza
February 23, 2021, 04:09 AM
Applying a solidly grounded wire immediately after performing a high-potential test:
The hipot test is a nondestructive test that determines the adequacy of electrical insulation for the normally occurring over voltage transient. This is a high-voltage test that is applied to all devices for a specific time in order to ensure that the insulation is not marginal.

Hipot tests are helpful in finding nicked or crushed insulation, stray wire strands or braided shielding, conductive or corrosive contaminants around the conductors, terminal spacing problems, and tolerance errors in cables. Inadequate creepage and clearance distances introduced during the manufacturing process.

Used the given blow link all information here !Thank You

https://electrical-engineering-portal.com/what-is-hipot-testing-dielectric-strength-test

SecondGen
February 23, 2021, 08:17 AM
The hipot test is a nondestructive test that determines the adequacy of electrical insulation for the normally occurring over voltage transient.

This is a bit misleading, I would say a hipot can be a destructive test.

trapnikas88
February 24, 2021, 10:40 AM
This is a bit misleading, I would say a hipot can be a destructive test.

Agreed. For instance, A VLF hi-pot test is less destructive, but can still damage a cable if there is a pre-existing condition. A DC hi-pot test is a destructive test for cables, not only in bringing out a fault in a cable but also the adding stress on the cable itself.

ethoenes
July 8, 2021, 02:50 PM
I saw this question and answered "Will ensure immediate personally safety." I didn't see it show up in my wrong answers.

I answered "Will Ensure immediate personally safety" and the answer was not correct.

bec51392
July 10, 2021, 12:21 PM
Applying a solidly grounded wire immediately after performing a high-potential test:
Your Answer: Will ensure immediate personally safety.
Correct Answer: May damage the insulation under test.

I cant find anything that supports this. Everything I read says ground it after....

Kalbi_Rob
July 11, 2021, 10:36 AM
Applying a solidly grounded wire immediately after performing a high-potential test:
Your Answer: Will ensure immediate personally safety.
Correct Answer: May damage the insulation under test.

I cant find anything that supports this. Everything I read says ground it after....
IEEE 400.1:

4.1 Test precautions:
Breakdown or terminal flashover may generate traveling waves up and down the cable that can be of a
magnitude great enough to cause degradation of the insulation of the cable or accessories or breakdown
of the cable insulation or the test source. A damping resistor or energy absorbing resistor in series with
the output of the dc test source rated for the reflected test voltage and energy stored in the cable if a
flashover occurs should be installed to isolate the dc test source from the test load. This resistor, if
properly sized, may protect the test source from overvoltages by absorbing the energy in the test circuit
and can reduce the oscillation amplitude of the traveling wave.

3.2.3 Discharge resistor
A resistor with a resistance not less than 5000 Ω/kV of test voltage is recommended to be used to discharge the
cable system after testing. This resistor should be designed to withstand the full test voltage without flashover
and to handle the discharge energy without overheating. An insulating grounding stick rated for the full test
voltage and a flexible conductor should be provided to connect the resistor across the cable circuit and ground.

bec51392
July 11, 2021, 08:45 PM
400.1
4.3 bottom of page 15 to top of 16

At the completion of the test period, the voltage can be reduced by returning the voltage control of the test equipment to zero. The voltage on the cable will discharge through the internal resistance of the test equipment. Normally this resistance has a very high ohmic value and the discharge time will be very long, especially for cables longer than a few 100 m. A long discharge time may be impractical. Further, directly grounding the cable with zero resistance while the voltage is at an elevated voltage can damage the cable. in order to discharge longer lengths of cable safety, separate automatic grounding systems with built in high voltage discharge resistance designed to provide a time constant of several seconds or longer can be used. In all cases, discharge mechanisms should be designed to safely handle the test voltage and energy stored in the cable under test.

After the test voltage is reduced to a low level, the high voltage conductor should be solidly grounded.

SecondGen
July 14, 2021, 10:45 AM
Applying a solidly grounded wire immediately after performing a high-potential test:
Your Answer: Will ensure immediate personally safety.
Correct Answer: May damage the insulation under test.

I cant find anything that supports this. Everything I read says ground it after....

You guys have already found the standards but I'll just add, I've seen nasty cable discharges back in the old days of DC hipoting. Terminations can easily be damaged if you don't give it some time (4x test period was the rule of thumb) or use a discharge stick. Some guys just attached a rubber bungie cord to a ground, they have about 8 ohms resistance.

Kalbi_Rob
July 18, 2021, 08:47 AM
You guys have already found the standards but I'll just add, I've seen nasty cable discharges back in the old days of DC hipoting. Terminations can easily be damaged if you don't give it some time (4x test period was the rule of thumb) or use a discharge stick. Some guys just attached a rubber bungie cord to a ground, they have about 8 ohms resistance.

After discharging with a homemade ground stick, I would apply electric fence wire to the terminals and ground and leave for the electricians to remove. I've seen cables (~2000ft long or more) build a charge after 24 hrs grounded.

SecondGen
July 18, 2021, 10:13 AM
After discharging with a homemade ground stick, I would apply electric fence wire to the terminals and ground and leave for the electricians to remove. I've seen cables (~2000ft long or more) build a charge after 24 hrs grounded.

Another great point, can also confirm long cable runs will rebuild a charge. I've even seen this happen on low voltage cable too but not as severe as MV. It's a good idea to leave cables grounded with some bare wire for the next guy, if possible.

When you don't have wire, you can even just lay the exposed conductor against the equipment enclosure or ground bus, anything helps. Nobody wants to be responsible for having someone get bit.

Izeldeen
November 6, 2021, 06:52 PM
Applying a solidly grounded wire immediately after performing a high-potential test:

it cause damage to the cable you just test