View Full Version : NETA Level 2 exam XFMR tables
Skoivisto
February 16, 2021, 05:05 PM
9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
Your Answer: 1 Gigohm
Help: NETA Table 100.5 (2019)
The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
akumaleon
February 16, 2021, 10:29 PM
9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
Your Answer: 1 Gigohm
Help: NETA Table 100.5 (2019)
The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
1G would be for liquid filled.
I would recommend understand the SI units prefixes too.
500
https://www.google.com/url?sa=i&url=https%3A%2F%2Fwww.youtube.com%2Fwatch%3Fv%3DUw YVQgYI8yE&psig=AOvVaw3fgJ0VjMptn9Pw_zyRorjD&ust=1613622269907000&source=images&cd=vfe&ved=0CAIQjRxqFwoTCIiMtsSJ8O4CFQAAAAAdAAAAABBL
Kalbi_Rob
February 17, 2021, 07:15 AM
9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
Your Answer: 1 Gigohm
Help: NETA Table 100.5 (2019)
The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
5000 Megohms is 5 gigohms. For a dry-type transformer rated 601-5000V, minimum resistance is 5000 Megohms or 5 Gigohms
emark4666
February 19, 2021, 12:34 PM
9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
Your Answer: 1 Gigohm
Help: NETA Table 100.5 (2019)
The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
5,000 Megohms is 5 Gigohms .
archieb7
February 21, 2021, 03:45 PM
9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
Your Answer: 1 Gigohm
Help: NETA Table 100.5 (2019)
The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
5 Gig.
rmr660
March 19, 2021, 01:58 PM
9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
Your Answer: 1 Gigohm
Help: NETA Table 100.5 (2019)
The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
1 gig is equal to 1,000 meg. as is 5 gig to 5,000 meg. It is sort of a trick question, just to make you keep on your toes.
Izeldeen
November 7, 2021, 08:36 PM
9. What is the NETA Recommended Minimum Insulation Resistance value for a dry-type 4,160V-480V D-D transformer primary winding?
Your Answer: 1 Gigohm
Help: NETA Table 100.5 (2019)
The answers were all in Gigs...1, 5, 10, 20. The cited table doesn't recommend anything beyond Megs...what am I missing?
5000Mega=5Gega
Powered by vBulletin® Version 4.2.5 Copyright © 2025 vBulletin Solutions Inc. All rights reserved.