PDA

View Full Version : Dear NETA. I Passed!!



A_Powers1992
December 15, 2021, 08:22 PM
Dear NETA,

A few months ago I posted these questions under the thread **Remembered NETA 2 questions**. After soaking in all input from this forum (thank you to ALL who contributed to my posts) and continuing my education on items I was not that familiar with, I can successfully say I passed your NETA 2. It was a daunting task and my brain hurts from all the information I have gone over the past few months. After my wife almost left me because my head was more concentrated on your standards, rather than her attention, I now understand the concept.
It truly does take FIELD EXPERIENCE to pass this test. IF you are a new tech to the industry, do not get discouraged if you fail this test once, twice, three times, or in my case, 4 times! It took getting jobs that actually work on the equipment listed to retain the knowledge I finally know. I have been with a NETA firm for 5 years. Before that, I was a journeyman-lineman with an added 5 years. 10 total in the high voltage electrical industry. I had almost given up on the thought of passing this test. However, with patience comes reward.
You WILL feel like this test is too much! Dear NETA, IT IS!!

There is no way to your standards that a 2 year man/woman should know the required knowledge to pass this test. I understand I may receive backlash from this, but give us a break. I actually studied more NETA 3 questions than NETA 2 and I feel that is how I was able to pass this test. When these standards were written, it was the technological ice age. I understand they are updated. But so it my IPhone X. Now, every technician is equipped with a computer, smart phone, and all the resources available to him/her so that whatever standard is required, we can easily find the information within a matter of minutes. Can we not come to terms with a society that is so technologically advanced that we can't even consider a vote on "open book" for some tests?

I have not posted these questions as a "cheat sheet". My integrity and willingness to find this information on my own should show my willingness to thrive in this fast paced, sleep-deprived trade.

Every NETA company can tell you finding help is scarce, especially in this economy. I urge any NETA member reading this to consider the future of this business. Help us help you. Word on the street is that you revamped the NETA 2 test because one lackluster company was caught cheating. Must we and all future technicians suffer from the mishap of one company? Or can you come to terms with the new age and allow anyone with a drive for excellence and a willingness to learn overcome such a complicated, extensive test?

Either way.

I passed. On to your level 3!



A multimeter is device that is connected:

Low impedance, series
Low impedance, parallel
high impedance, series
high impedance, parallel (correct answer)

Blow out coils are found on AIR circuit breakers

Puffer tubes are found on AIR circuit breakers to aid in the extinguishing of the arc.

Thermography scans require minimum 40% load.

>15 C in a thermography scan denotes major discrepancy; repair immediately.

SAE 5 Bolt (know what it looks like)

Highest pickup for LV-480 system ground?

600A
800A
1000A
1200A (Correct Answer)

Why do an insulation test between the neutral and ground?
To ensure that no other grounds are landed which could result in GF sensitivity

Interlock on MV MCC between switch and contactor. Why?
The interlock prevents the switch from being opened while the contactor is closed!

Which gauge should be recorded in oil sample report so that can be verification of moisture/no moisture in XFMR paper?
Oil Temperature

What is the role of a VFD?
To control the speed of AC induction motors.

27 device
Undervoltage

51:Time overcurrent
50: Instantaneous Time Overcurrent
52: AC Circuit Breaker
59: over voltage
86: Lockout
***87: Differential: The question on the test gives you a schematic with a picture of an 87 relay (with other ANSI device numbered symbols.) Along with that picture you’ll have two lines that go to two different CTs. The question will be, what CTs are associated with the differential relay? If you know 87 is differential relay, you’ll know what it feeds. In my case, it was an 800:5 CT and a 1200:5 CT)
37: Undercurrent
47: Phase Sequence Voltage Relay

13.8 Rated voltage. What minimum insulated gloves?
Class 2

Unit for Apparent Power?
VA

At what level does ventricular fibrillation occur?
100 mA-2000 mA

Testing circuit motor circuits would best be achieved by use of?

Ohmmeter (Correct Answer)
Phase-angle meter
Ammeter
Megometer

The Standard for Testing UPS batteries is:
IEEE 450

Insulated Gloves should be electrically tested every:
6 months

Disadvantage of (dc) hipot testing while testing MV shielded cables:

can’t detect faults
cant detect high impedance
requires high amounts of voltage (correct answer)
test set not easily portable

Which of the following is not required by NETA-ATS for AC induction motors?
Power factor

What are considered Network protectors?

A network protector is a special self-contained air breaker or switching unit having a full complement of current, potential and control transformers, as well as relay functionality.

Batteries are measured in Amp/hours

The unit for arc flash is calories per centimeter squared.

You arrive to find a MV circuit breaker open. At the mechanical switch to the unit, you see the mechanical switch open with a red flag. What would this indicate?

The breaker lost control power
The breaker was opened with the mechanical switch (correct answer)
The open signal was the last command given
The mechanical indicator is no good

What test is required for a 15 KV switch

Hipotential (Correct Answer)
power factor
TTR
Excitation

Which Transformer test could magnetize the windings?
PF
TTR
Excitation (Correct Answer)
Zero Sequence Impedance

Know what a tap changer looks like in a XFMR.
Picture of a DETC

If a motor and chain are present on an OLTC, once the tap is raised to the highest level and its still giving a raised signal, what should the motor OLTC do?

motor should stop, stay at highest level (Correct Answer)
motor continue til raise signal is gone
motor continue in reverse til back to neutral
motor stop, cool down

If a circuit is de-energized, locked-out, but NOT verified zero voltage and no protective grounds are in place the work is considered:

NOT in a work-safe condition

Arcing in oil sample represents what chemical.
Acetelyne

Batteries can produce dangerous levels of hydrogen.

Outdoor switchgear visual, mechanical inspections.
Clean insulators

Outdoor panel class is:
3R

For a switchgear space heater, according to Ohms Law as the voltage of the unit increases, the current decreases.

Which has the greatest TIME difference?
Extremely inverse
Inverse
moderately inverse
slightly inverse

Micro ohms to Ohms.
256 micro-ohms is .000256 ohms

System voltage could be read through a micro processing relay by which of the following?
PTs (Correct Answer)
CTs
Phase Angle
Main Breaker interrupting current


How could you recognize the difference between fiber optic cables and insulated cables?

insulated cables are shield
fiber optic cables require light to admit information
fibers optic cables are flexible
fiber contains RJ45 terminations (Correct Answer)

Which type of cables if used for LV conductors?

THHN (Correct Answer)
SIS
RH
MV-905

What type of switch is best used for commercial/light industrial services rated 2000/4000 amps?

Safety switch
Metal enclosed interrupter
Bolted pressure (Correct Answer)


86 is a lockout relay

According to NETA MTS-2019, what is the test voltage for a dc hipot voltage for a 15 KV SWTCH?
28.8 (Correct Answer)
34.4
18
64


When taking MTS oil samples in the field on an oil filled apparatus, bubbles in an oil sample:

Should be removed by the oil sample testing firm before testing
should be removed immediately (Correct Answer)
should not be removed before shipping to testing firm
are acceptable to certain limits

During ATS testing, fuse readings on a MV Fused Switch deviate by than 30%. What is the NETA-recommendation?
Replace
Inspect (Correct Answer)
Verify
FUSES Should not deviate by more than 15%


***49.) Low resistance ohm (contact resistance) readings should not deviate 50% from the?
Highest reading
mean reading
lowest value (Correct Answer)
median value

***50.) The small notch in a fuse is for what?

A rejection feature is used to prevent fuses with a lower voltage or interrupting rating (such as Class H and Midget fuses) from being used in a circuit that needs a higher rating. Class R and CC fuseblocks incorporate a built-in rejection feature while Class J and T blocks reject based on physical size

On a window CT with primary power going through H1-H2, What terminal will the secondary voltage exit from?

A) Line Side
B) Load Side
C) X1 (Correct Answer)
D) X2

Applying a solidly grounded wire immediately after performing a high-potential test:
Will ensure immediate personally safety.
May damage the insulation under test. (Correct Answer)


Which of the following is LEAST likely to contain a blown fuse trip device?
A. molded case circuit breaker
B. 360 amp 4.16 KV motor starter
C. low voltage power circuit breaker
D. 200 amp fused safety switch (Correct Answer)
E. none of the above

Transformer polarity is best achieved by reading between:
H1-H2
H0-X0
H1-X1 (Correct Answer)
X1-X2

TTR calculation on a DELTA-WYE Transformer

3 Problems on Power Triangle(Find KVAR) a squared + b squared= c squared

Grounding (Main Bonding Jumper)

SecondGen
December 16, 2021, 07:10 AM
Someone needs to buy this man a beer for such an open and honest testament. I'm sure many can relate.

Congratulations on your achievement.

ZachOlivier
December 17, 2021, 08:02 PM
Great stuff here, I remember some, if not most of these from my NETA 2 test.. I take my NETA 3 Monday, lets see how it goes

EricGoetz92
December 28, 2021, 08:56 AM
The question reads:

How could you recognize the difference between fiber optic cables and insulated cables?

I forget the answer options, but none of them really made sense and the correct answer was "fiber optic cables use RJ45 terminations", which is flat out wrong. An RJ45 is used on copper ethernet cables. I have no idea what this question should actually be so I have no idea how to fix it. Was someone trying to remember something they saw (and didn't understand at all) on the exam and came up with this? Was the original question "How could you recognize the difference between fiber optic and ethernet cables?" and the correct answer is "ethernet cables use RJ45 connectors"? Regardless, this question should get overhauled or just deleted.

Mark223
December 30, 2021, 06:28 PM
You post help alot. I just did my today and pass. 😊😊. I think about 20+ of the question here was on my. They kind of re-word the question a little bit but the answer was like word by word.

So for people taking there, i said do the testguy quiz. That also help me alot. GL

gusmoizoos
January 25, 2022, 02:19 PM
At what level does ventricular fibrillation occur?
100 mA-2000 mA



This is incorrect. Right from TestGuy "How Electricity affects your body"

'Ventricular fibrillation occurs with currents as low as 60-100 mA in AC systems. For DC, about 300 to 500 mA.'

DLWood
February 3, 2022, 12:47 PM
I'm preparing for NETA 2 and i've done several practice tests and its good to hear someone elses story.

Csloat217
February 3, 2022, 08:47 PM
Congratulations man! Thank you for giving back by uploading the questions you remembered. As someone new to the industry it's great to hear about people going at it until they pass!

dixontarave
February 6, 2022, 10:36 AM
Congratulations on your achievement.

A_Powers1992
February 24, 2022, 06:53 AM
Great stuff here, I remember some, if not most of these from my NETA 2 test.. I take my NETA 3 Monday, lets see how it goes

Based on your experience with the level 2 test, how did your level 3 test go sir?

A_Powers1992
February 24, 2022, 06:54 AM
You post help alot. I just did my today and pass. 😊😊. I think about 20+ of the question here was on my. They kind of re-word the question a little bit but the answer was like word by word.

So for people taking there, i said do the testguy quiz. That also help me alot. GL

Soo glad it helped!! That's awesome! Congrats on your level 2!!

BruceG400
March 18, 2022, 08:32 PM
Congrats on passing.

Kmuir2308
April 28, 2022, 12:48 PM
You post help alot. I just did my today and pass. 😊😊. I think about 20+ of the question here was on my. They kind of re-word the question a little bit but the answer was like word by word.

So for people taking there, i said do the testguy quiz. That also help me alot. GL
Hey how many questions were on the NETA 2 exam? Thanks

JacobG77
May 13, 2022, 08:55 AM
Just passed the NETA 2 on Tuesday, 5/10/2022. I have only been in this field for 2 years, actually less and had relatable experience with the electrical field. Some say you need more than 2 years for this test, but that is not true. Everyone retains and learns at different speeds. A decent amount of field experience is required, along with studying. All I am saying is if you retain and study decently well, and have been out in the field, you can most definitely reach this level, or pass this test in the 2 years required it takes to sign up. Things that I studied intensely were the ATS/MTS. I learned how to do calculations for KVA,KVAR, and Watts (Power Triangle). Basics of transformers, such as TTR calculation and Delta/WYE basics of Phase/Line Voltage. Only had a few ANSI device number questions, maybe 2, but I learned them anyways. Glove Classes. Bolt grades and sizes. A few basic safety questions. Learn how to read basic schematics. I also found a thread on here where the title is Passed NETA 2!! or something similar, where the guy remembered about 15 questions or so, and almost all are provided with the correct answers, and I actually saw most of the questions on the actual test. That most definitely helped me ace a few questions. If you get a basis of the things mentioned beforehand, you should be fine. I read the ATS/MTS through and through 2 to 3 times, and also memorized some of the basic tables in the back such as test voltages for electrical apparatus and test voltages for cables, and test voltages for transformer and size. Study well and dont psych yourself out, it aint nothing but a thing. Good luck fellow testers.

JacobG77
May 13, 2022, 08:59 AM
Thank you for posting this, those questions you posted were a crucial help to me. Just wanted to say thanks and youre the man.

JASONDOLANSKY
July 5, 2022, 01:12 PM
I agree one should not be required to memorize anything, but rather be able to navigate through the material and acquire the correct answers. Especially since everything is available at your fingertips now.