View Full Version : NETA IV Practice Exam Questions - 2022



nbernard
February 25, 2022, 06:26 PM
See practice questions below:

Feel free to provide input on solutions

nbernard
February 25, 2022, 06:31 PM
When performing maintenance on a 5kV class fuse interrupt switch. ANSI/NETA specifications require that the fuse resistance be measured. For a typical 200E fuse on the primary switch of a 1000 kVA, 4160V transformer, the technician would expect an approximate value of:

(A) 2000 microhms
(B) 200 microhms
(C) 20 microhms
(D) 200 millohms

nbernard
February 25, 2022, 06:33 PM
The sampling valve for a class 1 insulating oil transformer is located at the bottom of the transformer because the specific gravity of oil is:

(A) 1.0
(B) 1.21
(C) 0.91
(D) 0.65

nbernard
February 25, 2022, 06:33 PM
A technician is testing each of the protective elements of a microprocessor-based relay on a circuit breaker. The supervisor informs the technician that the breaker does not have be re-closed every trip because:

(A) During functional testing each trip path only needs to be tested once
(B) Testing the breaker trip string is not a required test as part of the protective relay functional test plan
(C) Tripping the breaker for each protective element is unlike real world conditions
(D) The close coil may be damaged by repeated operation

nbernard
February 25, 2022, 06:34 PM
Which of the following should be found during a visual inspection of the construction and installation of a self-cooled outdoor bus?

(A) A vapor barrier between connected indoor and outdoor bus sections
(B) A forced air rating if constant current rating is above 20, 000A
(C) Positive pressure monitor if current rating is above 20, 000A
(D) Desiccant filter if constant current rating is above 20, 000A

nbernard
February 25, 2022, 06:34 PM
NETA MTS requires that Load flow studies performed in accordance with

(A) IEEE 242
(B) IEEE 399
(C) IEEE 433
(D) IEEE 839

nbernard
February 25, 2022, 06:35 PM
Which electrical component is a source of fault current for incident energy calculations?

(A) Variable frequency drive
(B) Synchronous motor
(C) Network protector
(D) Load tap changer

nbernard
February 25, 2022, 06:36 PM
In accordance with ANSI/NETA ATS, the required insulating gas tests on an SF6 switch include moisture, dielectric breakdown, SF6 decomposition products and

(A) Air
(B) Interfacial tension
(C) Specific gravity
(D) Flammable gasses

nbernard
February 25, 2022, 06:36 PM
Which grounding system enhancement technique is considered permanent without requiring future maintenance?

(A) Chemical electrodes
(B) Conductive cement encased rods
(C) Bentonite clay encased rods
(D) Magnesium salt soil additive

nbernard
February 25, 2022, 07:03 PM
A technician measuring the power loss (dBm) of a 1000’ run of multimode fiber-optic cable obtained results below the minimum signalling threshold of the receiving equipment which has been running for several years. A second test result was different but also below the signalling threshold. The most likely issue is the

(A) Fiber power meter is defective and a new meter needs to be utilized to complete the measurements
(B) Fiber termination is loose, leading to poor connection between the test light source and receiver
(C) Transmitting equipment uses a higher power light source than reported which overcomes the dBm losses
(D) Fiber power meter was never calibrated for loss on a reference cable before testing for power loss

nbernard
February 25, 2022, 07:45 PM
1. What is the standard float voltage in terms of volts-per-cell in a lead-calcium battery?

(A) 0.8-0.85
(B) 1.4-1.42
(C) 2.12-2.15
(D) 2.17-2.25 <-


3. Transition impedance is a vital design characteristic of
(A) current limiting circuit breakers
(B) transformer differential protection schemes
(C) online load tap changers <-
(D) across the line motor starters



4. The predominant standards organization covering SCADA, RTU, and DCS systems is:

(A) IEEE
(B) NEMA
(C) IEC <-
(D) ICEA

5. Which of the following statements below is true with respect to circuit breakers rated for generator protection application?

(A) Short circuit duty cycle is required to be designed for CO – 30 sec – CO
(B) Continuous current rating must be 125% of the rating of the generator
(C) Transient recovery voltage testing must be performed for generator and system source faults
(D) Design tests must demonstrate the ability to interrupt 5 full short circuit faults

6. According to the 2018 NFPA 70E which method below is valid to verify the absence of voltages with a permanently mounted type of device?

(A) There is not a method that can be used that is a permanently mounted device. Therefore the technician must use either a direct contact device or a proximity device to verify the absence of voltage
(B) A fixed device can be used if it is permanently mounted, used only for voltage detection, listed for verifying absence of voltage, must measure all phase to phase and phase to ground voltages and must be verified as operating correctly
(C) The technician can simply use the voltmeter on the gear that measures voltage phase to phase and phase to ground for all voltages. Once verified that there is absence of voltage the technician can proceed.
(D) The technician can simply use the voltmeter on the gear and measure the voltage phase to phase and once verified at zero volts, begin work

7. When performing maintenance on a 5kV class fuse interrupt switch. ANSI/NETA specifications require that the fuse resistance be measured. For a typical 200E fuse on the primary switch of a 1000 kVA, 4160V transformer, the technician would expect an approximate value of:

(A) 2000 microhms
(B) 200 microhms
(C) 20 microhms
(D) 200 millohms

8. The sampling valve for a class 1 insulating oil transformer is located at the bottom of the transformer because the specific gravity of oil is:

(A) 1.0
(B) 1.21
(C) 0.91 <-
(D) 0.65

9. A technician is testing each of the protective elements of a microprocessor-based relay on a circuit breaker. The supervisor informs the technician that the breaker does not have be re-closed every trip because:

(A) During functional testing each trip path only needs to be tested once
(B) Testing the breaker trip string is not a required test as part of the protective relay functional test plan
(C) Tripping the breaker for each protective element is unlike real world conditions
(D) The close coil may be damaged by repeated operation

10. To increase the power factor of a substation 750 kVA load that has a 0.76 PF to a PF of 0.95, which of the following capacitor banks would provide desired power factor?

(A) 200 kVAR
(B) 250 kVAR
(C) 300 kVAR
(D) 450 kVAR

11. Which of the following should be found during a visual inspection of the construction and installation of a self-cooled outdoor bus?

(A) A vapor barrier between connected indoor and outdoor bus sections
(B) A forced air rating if constant current rating is above 20, 000A
(C) Positive pressure monitor if current rating is above 20, 000A
(D) Desiccant filter if constant current rating is above 20, 000A

12. NETA MTS requires that Load flow studies performed in accordance with

(A) IEEE 242
(B) IEEE 399 <-
(C) IEEE 433
(D) IEEE 839

13. Which electrical component is a source of fault current for incident energy calculations?

(A) Variable frequency drive
(B) Synchronous motor <-
(C) Network protector
(D) Load tap changer

14. In accordance with ANSI/NETA ATS, the required insulating gas tests on an SF6 switch include moisture, dielectric breakdown, SF6 decomposition products and

(A) Air <-
(B) Interfacial tension
(C) Specific gravity
(D) Flammable gasses

15. Which of the following is LEAST likely to be implemented on a modern low-voltage motor relay?

(A) Phase short circuit
(B) RTD overtemperature
(C) Current imbalance
(D) Sync-check <-

16. In accordance with ANSI/NETA ECS, when providing as-built drawings for commission project which of the following is true as it pertains to the disposition of as-builts?

(A) One package is left at the site and one retained by the commissioning company
(B) One package is submitted to the owner/operator and one package is retained by the commissioning company
(C) One pack is left at the site and one package is submitted to the owner/operator <-
(D) One package is left at the site and one package is submitted to the engineering firm

17. Which grounding system enhancement technique is considered permanent without requiring future maintenance?

(A) Chemical electrodes
(B) Conductive cement encased rods
(C) Bentonite clay encased rods
(D) Magnesium salt soil additive

18. Network protect trip actuator minimum pickup should be no more than

(A) 55% of control voltage
(B) 75% of control voltage <-
(C) 80% of control voltage
(D) 90% of control voltage
19. Which of the following is true regarding line sectionalizers?

(A) They have high interrupting ratings
(B) They are used with circuit reclosers <-
(C) They coordinate well with fuses
(D) They are used in transmission systems

20. Which of the following is a true statement in regards to the hotline tag of a circuit breaker?

(A) Locks recloser in the open position
(B) Limits fault current <-
(C) Prevents tripping due to inrush
(D) Prevents any close command

21. A technician measuring the power loss (dBm) of a 1000’ run of multimode fiber-optic cable obtained results below the minimum signalling threshold of the receiving equipment which has been running for several years. A second test result was different but also below the signalling threshold. The most likely issue is the

(A) Fiber power meter is defective and a new meter needs to be utilized to complete the measurements
(B) Fiber termination is loose, leading to poor connection between the test light source and receiver
(C) Transmitting equipment uses a higher power light source than reported which overcomes the dBm losses
(D) Fiber power meter was never calibrated for loss on a reference cable before testing for power loss

22. While conducting harmonic measurements on a new facility, which standard would delineate the requirements?

(A) NEMA
(B) ICEA
(C) IEEE <-
(D) NFPA

23. Storage batteries used as a source of power for emergency systems shall be suitable ratng and capacity to supply and maintain the total load for a minimum period of 1 ½ hours, without the voltage applied to load falling below

(A) 85.5% of normal
(B) 87.5% of normal <-
(C) 89.5% of normal
(D) 91.5% of normal

24. Which of the following types of relays could require a CT secondary connected to be wired in delta?

(A) Overcurrent
(B) Transformer differential
(C) Loss of field
(D) Reverse power

25. Which value is closest to the typical internal resistance of a current-limiting 15kV 100E fuse?

(A) 0.5 mohm
(B) 1.00 mohm
(C) 5.00 mohm
(D) 10.0 mohm

26. The voltage rating of a surge arrester installed on an ungrounded system over 1000V shall be equal to or greater than the continuous

(A) Phase-to-neutral voltage <-
(B) Phase-to-neutral voltage plus 10%
(C) Phase-to-phase voltage
(D) Phase-to-phase voltage plus 10%

27. In order to be considered “usual” service conditions AC induction motors must operate within what percentage of rated frequency?

(A) 5% <-
(B) 7%
(C) 9%
(D) 10%

28. To change taps under load for voltage regulation, load tap changers employ a transition impedance using a

(A) Reactance or resistance?
(B) Capacitance or inductance
(C) Reluctance and conductance
(D) Admittance and susceptance

29. Arriving at a power generation facility, a technician is told that the plant has lost power. The operators state nothing has been touched but the plant is without utility power and the SCADA systems are down until the system has been reset. Looking at the main switchgear, the following relay flags on the generator breaker are lit: 81-2, 32-1, 52-BF, 27-1. What should be investigated first?

(A) 81-2
(B) 32-1 or this one???
(C) 52-BF <-
(D) 27-1

30. Which of the following describes a line sectionalizer?

(A) Interrupts distribution line faults and separates the fault section.<-
(B) Has time/current characteristics to protect distribution lines
(C) Opens after specified number of faults are detected
(D) Clears distribution line faults and recloses a specified number of times

31. For network protectors, which of the following is an optional maintenance test?

(A) Verify current transformer ratios <-
(B) Measure the minimum pickup voltage of the motor control relay
(C) Measure resistance of power fuses
(D) Calibrate network protector relays

32. When performing winding resistance testing on a liquid filled transformer, what common temperature should the resistance measurement be corrected to?

(A) 25 C
(B) 40 C
(C) 75 C <-
(D) 100 C

nbernard
February 25, 2022, 07:46 PM
33. A plant has purchased a bank of power factor correction capacitors rated 600 kVAR at 12.47 kV. The system voltage is 4.16kV, however, a technician is asked to comment on the practicality of using the capacitors on a lower voltage. How would the technician advise the customer?

(A) The bank will last longer at the lower voltage and will still provide 600 kVAR of correction
(B) Capacitors cannot be used at voltages significantly different than rated
(C) The bank will only provide 150 kVAR at 4.16kV
(D) The bank will only provide 67 kVAR at 4.16 kV



34. Listed below are classes of transformer cooling systems. Which class is NOT matched with the correct type letter?

(A) OA – Oil-immersed, self-cooled
(B) OA/FA- Oil-immersed, self-cooled/forced-oil-cooled <-
(C) AA – Dry-type, self-cooled
(D) AA/FA – Dry-type, self-cooled/forced-air-cooled

35. If a watthour meter having a watthour constant of 3.6 is used with 600:5 ampere current transformers and 20:1 Potential transformers, the primary Kh is

(A) 21.6 watthours per revolution
(B) 4988 watthours per revolution
(C) 8640 watthours per revolution (3.6*120 *20) <-
(D) 43200 watthours per revolution

36. A technician measures the resistance of the insulation shield for a 200-foot run of 1/C 15kV 100 percent EPR 500 MCM copper tape-shielded cable with one splice. Phase A reads 0.7 ohms. This value is

(A) Too low
(B) Too high
(C) Subjective
(D) Satisfactory <-

37. NFPA 70, the National Electrical Code, requires ‘Inspections and Tests’ on equipment over 1000V. Where is this in the code?

(A) 110.16
(B) 225.56 <-
(C) 230.95
(D) 310.15

38. At which stage does the project electrical commissioning process begin?

(A) Construction
(B) Project planning
(C) Acceptance testing
(D) System energization <-






39. In accordance with ANSI/NETA MTS, which of the following tests is optional for automatic line reclosers?

(A) Remove a sample of the insulating liquid to test for color
(B) Perform at vacuum bottle integrity test
(C) Perform a power factor test on each pole <-
(D) Perform a dielectric withstand test on each pole

40. A 345 kV rated circuit switcher may employ a

(A) 3 gap SF6 interupter
(B) Single gap air interrupter <-
(C) Pre-insertion capacitor
(D) 2 cycle interruption capability

nbernard
February 25, 2022, 07:49 PM
Ignore earlier posts, did for post count

nbernard
February 25, 2022, 07:49 PM
One's without '<-' haven't found answers to them yet.

SecondGen
February 26, 2022, 09:32 AM
38. At which stage does the project electrical commissioning process begin?
(A) Construction
(B) Project planning
(C) Acceptance testing
(D) System energization <-


NETA Appendix A defines commissioning as "The systematic process of documenting and placing into service newly installed or retrofitted electrical power equipment and systems."

Under this definition, one could argue the "systematic process" begins at project planning. Also, is "documenting" considered acceptance testing? With this in mind I want to lean towards B or C.

SecondGen
February 26, 2022, 10:01 AM
Which grounding system enhancement technique is considered permanent without requiring future maintenance?
(A) Chemical electrodes
(B) Conductive cement encased rods
(C) Bentonite clay encased rods
(D) Magnesium salt soil additive


From what I understand, chemical electrodes have a service life of around 30-years minimum and are maintenance-free. Cement encased rods would be my second choice.

akumaleon
February 26, 2022, 05:41 PM
10. To increase the power factor of a substation 750 kVA load that has a 0.76 PF to a PF of 0.95, which of the following capacitor banks would provide desired power factor?
(A) 200 kVAR
(B) 250 kVAR
(C) 300 kVAR
(D) 450 kVAR

(C) 300 kVAR = 487-187


24. Which of the following types of relays could require a CT secondary connected to be wired in delta?

(A) Overcurrent
(B) Transformer differential
(C) Loss of field
(D) Reverse power

(B) Transformer differential <-Phase Angle Compensation


33. A plant has purchased a bank of power factor correction capacitors rated 600 kVAR at 12.47 kV. The system voltage is 4.16kV, however, a technician is asked to comment on the practicality of using the capacitors on a lower voltage. How would the technician advise the customer?
(A) The bank will last longer at the lower voltage and will still provide 600 kVAR of correction
(B) Capacitors cannot be used at voltages significantly different than rated
(C) The bank will only provide 150 kVAR at 4.16kV
(D) The bank will only provide 67 kVAR at 4.16 kV

(D) The bank will only provide 67 kVAR at 4.16 kV <- kvar output = (4.16 * 4.16 / 12.47*12.47) * 600

matlock59
February 27, 2022, 05:48 PM
A 345 kV rated circuit switcher may employ a:


3 gap SF6 interrupter
Single gap air interrupter
Pre-insertion capacitor
2 cycle interruption capability

epenland
June 29, 2022, 12:04 PM
A plant has purchased a bank of power factor correction capacitors rated 600 kVAR at 12.47 kV. The system voltage is 4.16kV, however, a technician is asked to comment on the practicality of using the capacitors on a lower voltage. How would the technician advise the customer?


The bank will last longer at the lower voltage and will still provide 600 kVAR of correction

Capacitors cannot be used at voltages significantly different than rated

The bank will only provide 150 kVAR at 4.16kV

The bank will only provide 67 kVAR at 4.16 kV