My boss and I meggered cables on a deenergized 1200A switchboard today with a mulitmeter, (set at 50v) fast and easy test, Phase to phase ( A-B, B-C, C-A, A-G, B-G, C-G. Make sure it's over 100mv and hold over a minute) went smooth but the inspector wanted to see if all cable lugs were torqued so a coworker went in to show him that they are but, applying 50v DC it caused it to energized it and feed back so he did get hit but nothing major, just a zap, he is okay. So, a way to deenergize it is to "ground it out", grab any size wire and safely tap the cable lugs the test were ran on. Point of this do not get comfortable because experience electricity does not care!!! stay safe.

Kalbi_Rob
April 14, 2022, 11:13 PM
My boss and I meggered cables on a deenergized 1200A switchboard today with a mulitmeter, (set at 50v) fast and easy test, Phase to phase ( A-B, B-C, C-A, A-G, B-G, C-G. Make sure it's over 100mv and hold over a minute) went smooth but the inspector wanted to see if all cable lugs were torqued so a coworker went in to show him that they are but, applying 50v DC it caused it to energized it and feed back so he did get hit but nothing major, just a zap, he is okay. So, a way to deenergize it is to "ground it out", grab any size wire and safely tap the cable lugs the test were ran on. Point of this do not get comfortable because experience electricity does not care!!! stay safe.

I highly recommend reading "A stitch in time" from Megger:
https://www.testequipmentdepot.com/megger/pdf/electrical-insulation-testing_guide.pdf

Also, when testing cable, always discharge the cable for atleast 4 time the time used to apply voltage:

"This stored energy, too, must be released at the end of a test, and requires a longer time than the capacitance charging current – about four times as long as the voltage was applied." -A Stitch In Time

SuspectK
April 19, 2022, 08:46 AM
What kind of cables were you megging at 50 Volts?