Core Subject 2 3
- Identify properties, types, and applications of switchgear and switchboard assemblies.
-
- IEEE C37.20.1 Standard for Metal-Enclosed Low-Voltage (1000 Vac and below, 3200 Vdc and below) Power Circuit Breaker Switchgear 2
- NEMA 250-2014 Enclosures for Electrical Equipment (1000 Volts Maximum) 2
- The Basics of Switchboards
- Rating of Ground Bus in Metal-Enclosed Switchgear
- Metal-Clad Switchgear or Metal-Enclosed Switchgear: Which Is It?
- Improving Safety with Arc-Resistant Switchgear
-
- Apply visual and mechanical inspections of switchgear and switchboard assemblies.
-
- NFPA 70 2017: Article 408 Switchboards, Switchgear, and Panelboards 2 3 4
- NFPA 70 2017: Article 110 Requirements for Electrical Installations: Working Space 2 3 4
- NFPA 70B: Chapter 15 Substations and Switchgear Assemblies 2 3 4
- Degradation of Power Contacts in Industrial Atmosphere: Silver Corrosion and Whiskers 3
- IEEE C37.20.6 Standard for 4.76 kV to 38 kV Rated Ground and Test Devices Used in Enclosures 4
- Top Five Switchgear Failure Causes and how to avoid them
- Condensation in Switchgear and Anticondensation Heaters
- Comparison of ANSI/IEEE Requirements for Low-voltage Switchgear
-
- Employ methods and procedures for electrical tests of switchgear and switchboard assemblies.
- Evaluate test results of switchgear and switchboard assemblies.
-
- NETA-ATS 2017: Section 7.1 Switchgear and Switchboard Assemblies 2 3 4
- NETA-MTS 2019: Section 7.1 Switchgear, Switchboard, and Panelboard Assemblies 2 3 4
-