    winding resistance tolerance for a transformer test

    Here is a question for you ,what is the winding resistance tolerance for a transformer test and what are you using as a reference for your answer.That was on the level four test.

  2. #2
  3. sepulveda7000 is offline
    NETA IV
    Junior Member
    Join Date
    Jan 2015
    Location
    Los Angeles, CA
    Posts
    2
    Reputation

    transformer winding resistance tolerance

    Quote Originally Posted by Larry5441 View Post
    Here is a question for you ,what is the winding resistance tolerance for a transformer test and what are you using as a reference for your answer.That was on the level four test.
    IEEE 62 Guide for Diagnostic Field Testing of Electric Power Apparatus - Part 1: Oil Filled Power Transformers, Regulators, and Reactors

    +/-5%

  4. #3
  5. Join Date
    Jan 2015
    Posts
    4
    Reputation
    Quote Originally Posted by sepulveda7000 View Post
    IEEE 62 Guide for Diagnostic Field Testing of Electric Power Apparatus - Part 1: Oil Filled Power Transformers, Regulators, and Reactors

    +/-5%
    You need to look at IEEE C57.12.90 it is a updated standard stating that winding resistance readings has no specific standards and will only be used as a reference .

  6. #4
  7. Join Date
    Dec 2014
    Posts
    11
    Reputation

    answer

    Quote Originally Posted by Larry5441 View Post
    You need to look at IEEE C57.12.90 it is a updated standard stating that winding resistance readings has no specific standards and will only be used as a reference .
    Adwell International LTD: If all readings are within one percent of each other then they are acceptable. Keep in mind that the purpose of the test is to test for gross differences between the windings and for opens in the connections.

  8. #5
  9. Join Date
    Jan 2015
    Posts
    4
    Reputation
    Quote Originally Posted by ruel guanzon View Post
    Adwell International LTD: If all readings are within one percent of each other then they are acceptable. Keep in mind that the purpose of the test is to test for gross differences between the windings and for opens in the connections.
    That was not the question ,it ask what was the tolerance differences not the goal of the test

  10. #6
  11. rgrabis is offline Junior Member Pro Subscriber
    Join Date
    Jun 2015
    Posts
    11
    Reputation
    So that's 5%, 1%, or "no standard" depending on the reference. The goal of the question may be for you to match the standard to the reference. I've also seen 1/2% for factory testing from Megger corp.

  12. #7
  13. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    According to Megger: The industry standard (factory) permits a maximum difference of 1/2 percent from the average of the three phase windings. Field readings may vary slightly more than this due to the many variables. If all readings are within one percent of each other, then they are acceptable.

    For the source document, see this thread -> http://testguy.net/threads/1497-Tran...stance-balance

Subscribe

Share this thread

Related Topics

  1. Transformer winding resistance, balance ?
    By rgrabis in forum Electrical Testing Talk
    Replies: 3
    Last Post: January 19, 2018, 11:34 AM
  2. 230kV Auto-Transformer (Insulation Resistance Test)
    By rizza_gay in forum Electrical Testing Talk
    Replies: 8
    Last Post: January 19, 2018, 11:27 AM
  3. winding resistance tester and CPC 100
    By moon1958moon in forum Electrical Testing Talk
    Replies: 8
    Last Post: August 4, 2017, 12:09 PM
  4. winding resistance of power transformers
    By Sanjayo in forum NETA Level 2 Exam
    Replies: 4
    Last Post: March 27, 2016, 07:13 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net