    Transformer Bushing and Oil Replacement methods

    Hello,

    Just curious to see if anyone has a best practice method for bushing replacement on a smaller distribution transformer. The oil will have to be drained, primary bushings replaced and new oil put back in for a 3MVA transformer and are looking for best practices with regards to keeping moisture out of the main tank while replacing the bushings. The bushings are inside the cable termination enclosure and are mounted horizontal. Any advice would be appreciated.

  2. #2
  3. Join Date
    Aug 2015
    Posts
    14
    Reputation

    Replaing bushing

    Quote Originally Posted by shawnroberts View Post
    Hello,

    Just curious to see if anyone has a best practice method for bushing replacement on a smaller distribution transformer. The oil will have to be drained, primary bushings replaced and new oil put back in for a 3MVA transformer and are looking for best practices with regards to keeping moisture out of the main tank while replacing the bushings. The bushings are inside the cable termination enclosure and are mounted horizontal. Any advice would be appreciated.
    Do not open the manhole if not required to limit the exposure to open air. If these are bolted in bushings and not welded then you should be to lower the oil level a little below the bushings. This will limit the exposure of the windings to open air. One thing that often helps is to have everything prepared to perform the bushing replacement so that the amount of time is as short as possible. I always liked to keep exposure time of the windings to a minimum.

    I would advise performing as found tests and as left tests to make sure that this work does not cause issues. I reviewed some data in which the technician forgot to connect the 3 low side bushings. The power factor was off and as you know the TTR and winding resistance failed. The sad thing is the the company who replaced the bushings was not the same company who came in behind them to test.

Subscribe

Share this thread

Related Topics

  1. Doble Testing a Bushing: C2 reading higher than nameplate
    By Bob_Woodward in forum Electrical Testing Talk
    Replies: 12
    Last Post: July 21, 2022, 04:45 PM
  2. 330kV Bushing PF values higher than benchmark
    By samkay in forum Electrical Testing Talk
    Replies: 1
    Last Post: April 8, 2020, 08:29 AM
  3. ATS 2017 Bushing power factor
    By burnettj1986 in forum NETA Level 3 Exam
    Replies: 1
    Last Post: July 16, 2019, 09:06 PM
  4. Primary current injection 138kV breaker with bushing CT's
    By david2458 in forum Electrical Testing Talk
    Replies: 1
    Last Post: April 12, 2018, 05:27 AM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net