Originally Posted by
TestTech
We have looked at it from a practical and economic angle:
Using LV breakers as an example, 600V equipment minimum Insulation Resistance is 100M per NETA. Typically the readings are much much higher of course. We use 1000V hand held meters that measure up to 4000M. If a LV breaker megs at 4000M we feel comfortable calling it good and enter >4000M on the test forms. Questionable readings would warrant using different equipment if necessary of course.
These handheld meters are true RMS DMM's with backlit screens, great battery life, incredibly rugged, read IR to 4000M and cost $160.00. A 5kV S1-1568 costs $5000.00. A set of test leads for a S1-1568 can cost 3X the cost of these meters.
A typical LV breaker project involves moving, racking, servicing large draw out 800A to 4000A power breakers, primary injection testing, Ductor etc. This is not the same as testing a 200A molded case breaker in a panelboard. The test equipment gets harsh duty. We would rather not trash a $5000 S1-1568 (and find out its broken on the next days job which involves a 20MVA Substation transformer where the Insulation Resistance readings actually do matter. The techs find it easier to use as you can perform other functions as well.
Most shops or techs will have their day to day equipment and "the good one" and know when to use each.
I guess I dont see the value in knowing the insulation resistance value of a LV circuit breaker was >7.5T if a value of >4000M is completely acceptable. We own many S1-1568 or similar 5kV Test Sets. We can and have used them on LV breaker projects but have chosen not to.
I would like to hear others views on this.