jrm5116
One way to do it is to convert the impedance percentage back to the actual impedance value to solve with the new voltage.
So from the nameplate SBase = 1000kVA and VBase = 34.5kV, then ZBase = VBase2/SBase
ZBase = 34.5kV2/1000kVA = 1190
Since the impedance is 5%, the actual impedance seen by the high side is
ZBase*5% or 1190*.05 = 59.5 Ohms
Now we just have an impedance and a voltage we are putting across it to find the current V=IR.
So VLN/R or I = (480/1.732)/59.5 Ohms = 4.65A
Another way to do this would be to find the primary side fault current at given levels, and multiply by the ratio of voltage you are applying.
IPrimary Fault @ 34.5 = 1000kVA/(34.5kV*1.732*.05) = 334.71A
334.71A * (480/34500) = 4.65A