    Question:
    1000kva 34.5kv to 480v secondary transformer 5% imp. Apply 480v to primary side and ground secondary. What is primary fault current?

    Answer: 4.65A

    I don't know what I am doing wrong, I am using the full load amps and fault current equations and I am not arriving at this answer.

  2. #2
  3. jrm5116 is offline Junior Member
    Join Date
    Aug 2021
    Posts
    10
    Reputation
    Quote Originally Posted by anderssok09 View Post
    Question:
    1000kva 34.5kv to 480v secondary transformer 5% imp. Apply 480v to primary side and ground secondary. What is primary fault current?

    Answer: 4.65A

    I don't know what I am doing wrong, I am using the full load amps and fault current equations and I am not arriving at this answer.
    One way to do it is to convert the impedance percentage back to the actual impedance value to solve with the new voltage.

    So from the nameplate SBase = 1000kVA and VBase = 34.5kV, then ZBase = VBase2/SBase
    ZBase = 34.5kV2/1000kVA = 1190
    Since the impedance is 5%, the actual impedance seen by the high side is
    ZBase*5% or 1190*.05 = 59.5 Ohms

    Now we just have an impedance and a voltage we are putting across it to find the current V=IR.

    So VLN/R or I = (480/1.732)/59.5 Ohms = 4.65A

    Another way to do this would be to find the primary side fault current at given levels, and multiply by the ratio of voltage you are applying.

    IPrimary Fault @ 34.5 = 1000kVA/(34.5kV*1.732*.05) = 334.71A

    334.71A * (480/34500) = 4.65A

  4. #3
  5. anderssok09 is offline Junior Member Pro Subscriber
    Join Date
    Dec 2020
    Posts
    6
    Reputation
    Quote Originally Posted by jrm5116 View Post
    One way to do it is to convert the impedance percentage back to the actual impedance value to solve with the new voltage.

    So from the nameplate SBase = 1000kVA and VBase = 34.5kV, then ZBase = VBase2/SBase
    ZBase = 34.5kV2/1000kVA = 1190
    Since the impedance is 5%, the actual impedance seen by the high side is
    ZBase*5% or 1190*.05 = 59.5 Ohms

    Now we just have an impedance and a voltage we are putting across it to find the current V=IR.

    So VLN/R or I = (480/1.732)/59.5 Ohms = 4.65A

    Another way to do this would be to find the primary side fault current at given levels, and multiply by the ratio of voltage you are applying.

    IPrimary Fault @ 34.5 = 1000kVA/(34.5kV*1.732*.05) = 334.71A

    334.71A * (480/34500) = 4.65A
    Thanks!

Subscribe

Share this thread

Related Topics

  1. Primary Current Injection instantenous Pickup
    By changeabilities in forum Electrical Testing Talk
    Replies: 15
    Last Post: February 26, 2021, 11:50 AM
  2. Learning how to primary current inject breakers
    By lazo2794 in forum Electrical Testing Talk
    Replies: 4
    Last Post: December 3, 2020, 07:53 PM
  3. Transformer Primary Fault Current
    By kchenoweth in forum NETA Level 4 Exam
    Replies: 3
    Last Post: August 22, 2020, 08:46 PM
  4. Replies: 12
    Last Post: July 28, 2020, 08:27 AM
  5. Primary Current Injection Test
    By changeabilities in forum Electrical Testing Talk
    Replies: 4
    Last Post: August 12, 2018, 08:17 AM
Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net