    Customer complaint: 86 lockout rolls to tripped position, breaker is open, load side of breaker has new ATS installed on load side of 4160D-480/277Y transformer. As of right now I see no reason to investigate the load side of the breaker. No flags from the electromechanical relays, (3) 50/51 and (1) 50G. Considering faulty 86 mechanism or control circuit? any thoughts?
  2. #2
  3. Join Date
    Jun 2016
    Posts
    11
    Reputation
    Quote Originally Posted by DLWood View Post
    Check the target coil tap. If it is set to 2 amps they usually won't drop on the current needed to roll a lockout coil. Mechanical targets can also be misadjusted and not drop. Don't assume the 86 is defective, if you don't do a thorough investigation and close in on a fault you will have lots of explaining to do.
Subscribe
Share this thread
Related Topics
  1. Load resistance
    By Vysakh9292 in forum NETA Level 2 Exam
    Last Post: June 22, 2022, 11:01 PM
  2. What is the combined load in KVA & PF?
    By SecondGen in forum NETA Level 4 Exam
    Last Post: June 28, 2020, 04:43 PM
  3. GE AK breaker intermittent nuisance tripping of bell alarm lockout
    By jdk0082 in forum Electrical Testing Talk
    Last Post: March 12, 2018, 02:26 PM
  4. Danger after lockout of GE Power Break equipped with electric charge
    By SecondGen in forum Safety and Arc Flash Talk
    Last Post: April 11, 2016, 02:38 PM
Follow us
Explore TestGuy
NETA Certification Training
NICET Electrical Power Testing
Help and Support
You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net