    How to reset solid state trip logs, sorted by manufacturer and trip unit type

    You should always reset the event log in solid state trip units after testing but unfortunately user manuals are not always available. This is an attempt to build a quick reference of solid state trip units and how to reset their trip log. This list will be updated periodically. Be sure to subscribe or bookmark for future use and feel free to reply with your contributions.


    General Electric

    EntelliGuard and MicroEntelliguard TU

    Reset event log
    1. Scroll to EVENT tab on main screen
    2. Press UP and DOWN arrows simultaneously
    3. Verify Event 0 is blank


    MicroVersaTrip Plus and PM

    Clearing the trip information
    • With the Trip Unit in Status mode, hold down the VALUE key and press the SELECT key. The trip information is then cleared and the display reverts to STATUS OK.

    Clearing the Trip Operations Counter
    • To clear a particular counter, first display the corresponding count, then hold down the VALUE key and press the SELECT key. The trip counter is reset to zero.


    Power+
    Trip Targets - To determine the condition causing a breaker trip, press the VIEW button. One of the three target LEDs will light. The RESET button clears the trip target indication.



    Utility Relay Company

    AC-Pro

    Clearing the Last Trip Data
    1. No security key jumper wire
    2. Press the REVIEW button to display the last trip data
    3. Push and hold both UP and DOWN buttons
    4. While still holding the UP and DOWN buttons, press the SAVE button
    5. Release all three buttons
    6. “NO LAST TRIP” is displayed



    EATON / Cutler-Hammer

    Digitrip models 1150, 1150i, 1150+, and 1150i+

    • No reset. The event data is stored in nonvolatile RAM and is maintained on a first-in, first-out basis.
    Last edited by SecondGen; March 2, 2016 at 04:59 PM.

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    update: added GE Power+ trip units

Subscribe

Share this thread

Related Topics

  1. What would cause a generator to trip on 32R?
    By djohnson18 in forum NETA Level 3 Exam
    Replies: 4
    Last Post: January 10, 2019, 11:28 AM
  2. Digitrip 1150 & 520 Trip Curve Calculator (Time Saver)
    By SecondGen in forum Technical Documents
    Replies: 0
    Last Post: September 7, 2016, 06:49 PM
  3. EATON Magnum DS with Digitrip 1150+ showing "TRIP" on the display
    By keith63c in forum Electrical Testing Talk
    Replies: 2
    Last Post: May 25, 2016, 02:03 PM
  4. Trip contact operation after relay testing
    By DetroitLions in forum NETA Level 3 Exam
    Replies: 0
    Last Post: January 30, 2016, 09:16 PM
  5. Tips for Westinghouse DH breakers that trip free or won’t close
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: May 10, 2015, 09:12 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net