    You should always reset the event log in solid state trip units after testing but unfortunately user manuals are not always available. This is an attempt to build a quick reference of solid state trip units and how to reset their trip log. This list will be updated periodically. Be sure to subscribe or bookmark for future use and feel free to reply with your contributions.
    General Electric
    EntelliGuard and MicroEntelliguard TU
    Reset event log
    1. Scroll to EVENT tab on main screen
    2. Press UP and DOWN arrows simultaneously
    3. Verify Event 0 is blank
    MicroVersaTrip Plus and PM
    Clearing the trip information
    • With the Trip Unit in Status mode, hold down the VALUE key and press the SELECT key. The trip information is then cleared and the display reverts to STATUS OK.
    Clearing the Trip Operations Counter
    • To clear a particular counter, first display the corresponding count, then hold down the VALUE key and press the SELECT key. The trip counter is reset to zero.
    Power+
    Trip Targets - To determine the condition causing a breaker trip, press the VIEW button. One of the three target LEDs will light. The RESET button clears the trip target indication.
    Utility Relay Company
    AC-Pro
    Clearing the Last Trip Data
    1. No security key jumper wire
    2. Press the REVIEW button to display the last trip data
    3. Push and hold both UP and DOWN buttons
    4. While still holding the UP and DOWN buttons, press the SAVE button
    5. Release all three buttons
    6. “NO LAST TRIP” is displayed
    EATON / Cutler-Hammer
    Digitrip models 1150, 1150i, 1150+, and 1150i+
    • No reset. The event data is stored in nonvolatile RAM and is maintained on a first-in, first-out basis.
  2. #2
  3. SecondGen's Avatar
    I push buttons.
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    update: added GE Power+ trip units
Subscribe
Share this thread
Related Topics
  1. What would cause a generator to trip on 32R?
    By djohnson18 in forum NETA Level 3 Exam
    Last Post: January 10, 2019, 11:28 AM
  2. Digitrip 1150 & 520 Trip Curve Calculator (Time Saver)
    By SecondGen in forum Technical Documents
    Last Post: September 7, 2016, 06:49 PM
  3. EATON Magnum DS with Digitrip 1150+ showing "TRIP" on the display
    By keith63c in forum Electrical Testing Talk
    Last Post: May 25, 2016, 02:03 PM
  4. Trip contact operation after relay testing
    By DetroitLions in forum NETA Level 3 Exam
    Last Post: January 30, 2016, 09:16 PM
  5. Tips for Westinghouse DH breakers that trip free or won’t close
    By SecondGen in forum Electrical Testing Talk
    Last Post: May 10, 2015, 09:12 AM
Tags for this Thread
Follow us
Explore TestGuy
NETA Certification Training
NICET Electrical Power Testing
Help and Support
You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net