Looking for high current testing standard for breakers

 Jump to latest post
Page 2 of 2 FirstFirst 12
    #11
  1. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    There isn't anything I know of that comes directly from NETA covering circuit breaker primary injection testing procedures. NETA specs usually tell you to consult manufacturers recommendations for specific procedures.
    Last edited by SecondGen; June 15, 2015 at 04:21 AM.

  2. #12
  3. CoDylan is offline
    Test Before Touch!
    Junior Member
    Join Date
    May 2015
    Posts
    2
    Reputation
    NETA Tests for Low-Voltage Power Circuit Breaker (LSIG):
    1. Determine long-time pickup and delay by primary current injection.
    2. Determine short-time pickup and delay by primary current injection.
    3. Determine ground-fault pickup and delay by primary current injection.
    4. Determine instantaneous pickup current by primary current injection.

    NETA Test Results for Low-Voltage Power Circuit Breaker (LSIG):
    1. Long-time pickup values should be as specified, and the trip characteristic shall not exceed manufacturer’s published time-current characteristic tolerance band.
    2. Short-time pickup values should be as specified, and the trip characteristic should not exceed manufacturer’s published time-current tolerance band.
    3. Ground fault pickup values should be as specified, and the trip characteristic should not exceed manufacturer’s published time-current tolerance band.
    4. Instantaneous pickup values should be within the tolerances of manufacturer’s published data.

    The reason why there is not a test percentage within the NETA specifications is that the expectation is the unit will function as specified at any point of the time-current curve or manufacturer's tolerance, not just at one specific value. Although it is common industry practice to test long time at 300% of pickup and short time and ground fault at 150% of pickup. Instantaneous is per the curve tolerance.

  4. #13
  5. Join Date
    Mar 2015
    Location
    Pittsburgh, PA
    Posts
    10
    Reputation

    ANSI/NETA ATS

    TABLE 100.7 deals with Inverse Time Trip Tests
    at 300% of Rated Continuous Current Molded-Case Circuit Breakers.
    Maximum trip times

  6. #14
  7. Join Date
    Mar 2015
    Location
    Pittsburgh, PA
    Posts
    10
    Reputation

    ANSI/NETA ATS cont.

    TABLE 100.8 deals with Instantaneous Trip Tolerances
    for Field Testing of Circuit Breakers

  8. #15
  9. Join Date
    Apr 2014
    Posts
    5
    Reputation
    NFPA-70B explains low voltage breaker testing a little clearer than NETA.

Page 2 of 2 FirstFirst 12
Subscribe

Share this thread

Related Topics

  1. Replies: 7
    Last Post: August 3, 2017, 03:38 PM
  2. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Technical Documents
    Replies: 3
    Last Post: June 11, 2015, 06:52 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net