    Looking for high current testing standard for breakers

    Does anyone have a standard for high current testing breakers ,I have not seen anything from NETA

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    what kind of standard are you looking for? I have some manufacturers field testing manuals that cover primary injection testing.

  4. #3
  5. Larry5443's Avatar
    Larry5443 is offline
    Cabinet Rat Neta Level 4
    Junior Member
    Join Date
    Apr 2014
    Posts
    18
    Reputation

    High current testing

    Long time is %300 or %600. There is nothing for short time and instantaneous is 10 times breaker rating ground fault is questionable

  6. #4
  7. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    Electronic Trip CB Primary Injection Procedure

    I was able to find a section from a Square D Field Maintenance Guide for electronic trip circuit breakers that covers performance testing. Looks like this might be what you are looking for, it has procedures for Long Time, Short Time, Instantaneous and Ground Fault as well as Insulation Resistance and Contact Resistance tests. See the document attached to this post. Hope this helps.
    Attached Files Attached Files

  8. #5
  9. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation

    LV circuit breaker primary current injection values

    Looks like long time is 300%, short time delay and ground fault are 150%, according to Square D. For instantaneous start at 70% of expected trip value and apply 10-cycle pulses as you raise current.

  10. #6
  11. Larry5443's Avatar
    Larry5443 is offline
    Cabinet Rat Neta Level 4
    Junior Member
    Join Date
    Apr 2014
    Posts
    18
    Reputation

    High current testing

    Are they saying that %150 for short time and ground fault is what calculation is it % 150 of what

  12. #7
  13. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    150% of the determined pickup value. All dependent on your trip settings at time of test.

    Quote Originally Posted by Larry5443 View Post
    Are they saying that %150 for short time and ground fault is what calculation is it % 150 of what

  14. #8
  15. Larry5443's Avatar
    Larry5443 is offline
    Cabinet Rat Neta Level 4
    Junior Member
    Join Date
    Apr 2014
    Posts
    18
    Reputation

    High current testing

    Can you explain with a formula please

  16. #9
  17. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Here is a quick example: If you had a 1000A circuit breaker with a short time pickup of 3X it should trip on short time around 3000A. You would first verify that by turning off I2t (if applicable) and ramp up current starting from about 2500A, the breaker should trip around 3000A. Next, turn I2t back on (if applicable) and preset your current to 150% of the pickup value (in this case: 3000A x 1.5 = 4500A). Initate current at that value and the breaker should trip within its specified time.

    Give that PDF a read, it is all explained in there stp by step.

  18. #10
  19. Larry5443's Avatar
    Larry5443 is offline
    Cabinet Rat Neta Level 4
    Junior Member
    Join Date
    Apr 2014
    Posts
    18
    Reputation

    High current testing

    I understand what you are saying ,Iam asking is there anything that is written as far as a standard from Neta or anyone else in the testing organization .

Page 1 of 2 12 LastLast
Subscribe

Share this thread

Related Topics

  1. Replies: 7
    Last Post: August 3, 2017, 03:38 PM
  2. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Technical Documents
    Replies: 3
    Last Post: June 11, 2015, 06:52 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net