    Help with power factor calculations, how to find KW from KVA and KVAR

    A single line feeds 2 separate loads. The first load is 1200kw at .80 pf. The second load is 800kva and 300 kvar. What is the total load on the single line feeder?

    I have been racking my brain trying to figure out this question that someone else said was on the Level 4 exam. My answer is 1702kW, can anyone let me know if I am right? Here is how I figured it out:

    Load 1: Easy, just correct kW for power factor. 1200 * 0.8 = 960kW

    Load 2: This is where it got tricky but this is how I was able to calculate kW from kVA and kVAR, I think:

    (800kVA)2 = 640000
    (300kVAR)2 = 90000
    640000 - 90000 = 550000
    Square root (550000) = 742kW

    Load 1 (960kW) + Load 2 (742kW) = 1702kW

    Just looking to know if this is correct. Thanks in advance.

  2. #2
  3. Join Date
    Jan 2015
    Posts
    26
    Reputation

    kva kvar kw calculation

    The equation is: KW = KVA x pf, therefore KVA = KW/pf
    1200 kW = KVA x 0.8 ..... KVA = 1200/0.8 = 1500 KVA,
    In other words, the 1200 kW, with pf 0.8, needs to have available 1500 KVA.

    For the second question we have:
    (KVA)2 = (KVAR)2 + (KW)2 .... (800)2 = (300)2 + (KW)2 (This is you got it right)

    Observe that you can use the above equation to calculate the KVAR for the first question:
    (1500)2 = (KVAR)2 + (1200)2
    KVAR = Square root ( 2250000 - 1440000) .... KVAR = Square root(810000) = 900
    Load: 1500 + 800 = 2300 KVA
    1200 + 742 = 1942 KW
    900 + 300 = 1200 KVAR
    Attached Thumbnails Attached Thumbnails KVA.jpg  


  4. #3
  5. Join Date
    Aug 2014
    Location
    Capital City
    Posts
    74
    Reputation

    how to find kvar

    doh! thats what i get for not double checking my work. thanks for clearing this up for me!

    Quote Originally Posted by joaogemal View Post
    The equation is: KW = KVA x pf, therefore KVA = KW/pf

  6. #4
  7. Join Date
    Dec 2014
    Posts
    57
    Reputation

    kva to kw

    No calculation is necessary for load 1, you are given the kW.

    Quote Originally Posted by veracon0700 View Post
    Load 1: Easy, just correct kW for power factor. 1200 * 0.8 = 960kW

  8. #5
  9. Join Date
    Jan 2016
    Posts
    5
    Reputation

    kvar kw

    i found this power factor triangle to be helpful in understanding these kind of calculations
    Attached Thumbnails Attached Thumbnails power-factor-1-400.jpg  


  10. #6
  11. Join Date
    May 2017
    Posts
    7
    Reputation
    Quote Originally Posted by veracon0700 View Post
    A single line feeds 2 separate loads. The first load is 1200kw at .80 pf. The second load is 800kva and 300 kvar. What is the total load on the single line feeder?

    I have been racking my brain trying to figure out this question that someone else said was on the Level 4 exam. My answer is 1702kW, can anyone let me know if I am right? Here is how I figured it out:

    Load 1: Easy, just correct kW for power factor. 1200 * 0.8 = 960kW

    Load 2: This is where it got tricky but this is how I was able to calculate kW from kVA and kVAR, I think:

    (800kVA)2 = 640000
    (300kVAR)2 = 90000
    640000 - 90000 = 550000
    Square root (550000) = 742kW

    Load 1 (960kW) + Load 2 (742kW) = 1702kW

    Just looking to know if this is correct. Thanks in advance.
    I guess you want to come up with all three values for both feeders to get all parameters of the load. In the case of the first load 1200KW at .8 - 1200/.8 = 1500KVA. The angle is 36.869 degrees so you have (sine) 900KVAR. Load 1 is fully described as 1500KVA, 1200KW, and 900KVAR.

    Load 2 at 800KVA and 300KVAR. The angle is ARC SIN 300/800 = 22.02 degrees. Watts then is 741.619 KW. Just add them all up for the total of each parameter. The assumption is that the vars and watt flow is in the same direction. Alternatively you can use the Pythagorean theorem for load 2 - that is 800(squared) = 300(squared) + x(squared) and you get the same 741.619 (as a cross check). www.cttestset.com

  12. #7
  13. Join Date
    May 2018
    Posts
    25
    Reputation
    Quote Originally Posted by veracon0700 View Post
    A single line feeds 2 separate loads. The first load is 1200kw at .80 pf. The second load is 800kva and 300 kvar. What is the total load on the single line feeder?

    I have been racking my brain trying to figure out this question that someone else said was on the Level 4 exam. My answer is 1702kW, can anyone let me know if I am right? Here is how I figured it out:

    Load 1: Easy, just correct kW for power factor. 1200 * 0.8 = 960kW

    Load 2: This is where it got tricky but this is how I was able to calculate kW from kVA and kVAR, I think:

    (800kVA)2 = 640000
    (300kVAR)2 = 90000
    640000 - 90000 = 550000
    Square root (550000) = 742kW

    Load 1 (960kW) + Load 2 (742kW) = 1702kW

    Just looking to know if this is correct. Thanks in advance.
    This question threw me for a loop at first, too. I saw the first numbers so I went ahead and calculated the kVA for 1200kW at 0.80pf. I used pythagorean theorem for the 2nd part of the question and then realized that I didn't need the kVA from the first part of the question. They had already given me the real power value. Oops.

  14. #8
  15. Join Date
    Apr 2018
    Posts
    65
    Reputation
    Great thread. I'm quite a ways off from even level 3, but like skipping ahead.

Subscribe

Share this thread

Related Topics

  1. Understanding power factor is easy when you relate it to beer!
    By veracon0700 in forum NETA Level 2 Exam
    Replies: 15
    Last Post: November 6, 2021, 06:41 PM
  2. Power Factor for New Mineral Oil
    By Salcama in forum NETA Level 3 Exam
    Replies: 4
    Last Post: February 22, 2020, 05:12 PM
  3. Replies: 9
    Last Post: August 16, 2018, 02:28 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net