Hi, everyone. I used a winding resistance tester to test 0.75 MVA transformer primary (13800-600). I got a unbalance phase resistance. H1-H2 WAS 2.6om AND H1-H3 WAS 3.8OM. H2-H3 WAS 8.7OM.
I DON'T THINK SOMETHING WRONG WITH THE TX, IT IS ACCEPTANCE TEST. I USED CPC-100 TO TEST TX AGAIN. I GOT EVERY PHASE WERE AROUND 2.6OM.
I THINK THE REASON FOR WINDING RESISTANCE IS THAT I DID NOT DISCHARGE THE TX AFTER H1-H2 TESTING AND STARTED TO TEST H1-H3 IMMEDIATELY. BUT THE CPC-100 DISCHARGE THE TX AUTOMATICALLY.
JUST REMIND TO DISCHARGE THE TX AFTER TEST.