Cable hi-pot withstanding time, why 15 minutes?

 Jump to latest post
Page 3 of 4 FirstFirst 1234 LastLast
    #21
  1. Join Date
    Dec 2014
    Posts
    57
    Reputation
    nobody said anything about doing what you feel. A gang test is a perfectly viable option unless specs say otherwise.

    Quote Originally Posted by DanielTronco View Post
    IEEE NETA ANSI and other standards exist for a reason. The 15 minutes has a purpose. Just test according to the spec and record your results. If your just looking to do whatever you feel like then what's the point of standards and procedures.

  2. #22
  3. Join Date
    Dec 2014
    Posts
    57
    Reputation
    LMAO, so true.

    Quote Originally Posted by Will Ward View Post
    You mean I can't just wave that NETA card over a broken breaker and it won't fix itself????

  4. #23
  5. Join Date
    Dec 2014
    Location
    Maryland
    Posts
    14
    Reputation
    I grew up in the utility world and was taught to "gang test". Nothing in NETA specs ever told me to test individual phases only. Acceptance tests are pass/fail only. As per NETA-

    "If no evidence of distress or insulation failure is observed by the end of the total time of voltage
    application during the test, the test specimen is considered to have passed the test."


    When contracted to perform Tan Delta VLF testing as a diagnostic test, of course you test individual conductors to assess splice, termination, and overall insulation condition when compared to the associated conductors.

    And in case you are wondering I passed Level IV and did not have to resort to cheating.

  6. #24
  7. Join Date
    Aug 2015
    Location
    Clute, Tx
    Posts
    10
    Reputation
    Quote Originally Posted by madMAX View Post
    tie all three cables together, do a gang test, and roll out early.
    Definitely this. Saves a lot of time, granted one of your cables isn't testing bad.

  8. #25
  9. Join Date
    Jun 2016
    Posts
    3
    Reputation
    Quote Originally Posted by ArchIsChompa View Post
    Definitely this. Saves a lot of time, granted one of your cables isn't testing bad.
    Assuming we are talking about solid dielectric cable systems, you should test the phases independently with a insulation resistance test. Since the actual resistance value has little meaning the best you can do on a 3 phase system is to compare the phases. I recommend a measurement after stable voltage or <1 minute. A VLF withstand test can be performed with all three phases connected since there is no insulation performance measurement.

    The major issue I have with this discussion, is that we are splitting hairs. An insulation resistance and VLF tests typically detect less than few percent of issues that do not meet the minimum performance requirements as per the cable and accessory manufacturers' QC specification. Just keep in mind that, while you can be reasonably confident that you will defect a failure (insulation rupture/short) in the cable system, these test are nearly helpless to find the vast majority of cable reliability issues. If you really need to determine a cable system's reliability, you are going to need a completely different type of test.


    Ben Lanz
    Past Chair IEEE 400

  10. #26
  11. Join Date
    Jul 2016
    Location
    Nashville, TN
    Posts
    2
    Reputation
    IEEE 400 is a go, no-go test. It states, "The system is required to withstand the specified voltage for the specified time duration. This test will normally reveal gross imperfections due to improper field handling, such as excessive bending or airgaps between the insulation and shield interfaces. While performing a high-voltage dc test, it is common to monitor insulation leakage current and/or insulation resistance. The guide notes that a decrease in current with time is generally a practical criterion for acceptance." 15 minutes was chosen to make rule out improper installation, air gaps, etc.. It was deemed that in this amount of time a problem will manifest itself.

  12. #27
  13. Join Date
    Jul 2016
    Location
    Manila, Philippines
    Posts
    3
    Reputation

    Cable Hi-Pot Testing

    Hi-potential can be performed on new cables, before it can be commissioned or put online, right. Is it still practical and or advisable to subject an old or in operation power cable to hi-pot testing? Will it not degrade or shorten it's life span?

  14. #28
  15. BrickSalad is offline Junior Member Pro Subscriber
    Join Date
    Oct 2015
    Posts
    11
    Reputation

    The 15 minutes thing...

    With regards to VLF hipot, I've got an excerpt from my company's literature (paraphrased of course) that might bear some light on the 15 minutes requirement:

    The results of field tests on over 15,000 XLPE cable circuits show that 68% of recorded failures happened within 12 minutes, 89% within 30 minutes, 95% within 45 minutes, and 100% after an hour. (Moh[B17])
    (I'm guessing here that these tests were run for an hour, hence the 100%.)

    So it actually makes sense to test a cable *longer* than 15 minutes if you really want to catch all of the cable faults. There is a balance between practicality and perfection however, and it seems like most companies go for 15 minutes. Detects 3/4 of defective cables without taking an unreasonably long amount of time. We sometimes run 1/2 hour or even full hour tests on cables at my company, but usually the customer only wants the standard 15 minute test.

    Hope that helps!

  16. #29
  17. Join Date
    Oct 2016
    Posts
    1
    Reputation
    Hi everyone..i am a new user here. As per my knowledge its true that you should wait the 15 minutes and also you should plot the readings that you take. I think you will observe the trend of the results, it will reduce quickly in the beginning and then start to level out at the end of the 15min period.

  18. #30
  19. Join Date
    Feb 2019
    Posts
    3
    Reputation
    15 minutes because some faults wont show right away and take some time under load

Page 3 of 4 FirstFirst 1234 LastLast
Subscribe

Share this thread

Related Topics

  1. Time Domain Reflectometer
    By adamwilson in forum NETA Level 3 Exam
    Replies: 4
    Last Post: July 26, 2018, 12:17 PM
  2. Replies: 2
    Last Post: July 5, 2018, 04:35 PM
  3. Westinghouse DS-206 complete dis-assembly in less than 10 minutes
    By SecondGen in forum Electrical Testing Talk
    Replies: 0
    Last Post: December 18, 2015, 03:21 PM
  4. time current curves for fedral pacific circuit breakers
    By Herc8306 in forum Technical Documents
    Replies: 3
    Last Post: June 11, 2015, 06:52 PM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net