    Question in question on the practice test

    I am new in this industry but am questioning an answer i got wrong on the practice test.

    Generally, when should circuit breaker contacts be lubricated?
    Your Answer: Circuit breaker contacts should not be lubricated.
    Obviously you see my answer of "contacts should not be lubricated", could this question be about hinge points that you would oil/lubricate. I asked a Level III I work with and he has never heard of lubricating the actual contacts. Does anyone have any clarification. Thanks in advance

  2. #2
  3. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    Circuit breaker contacts usually should not be lubricated. The heat from the current flow through the contacts breaks the lubricant down and causes contact resistance to increase. With that said, some manufacturers might recommend it.

    Check out this thread for more info -> http://testguy.net/threads/10-Do-You...se-CB-Contacts


    Quote Originally Posted by zofofg View Post
    I asked a Level III I work with and he has never heard of lubricating the actual contacts.
    Last edited by SecondGen; July 16, 2015 at 07:22 PM.

  4. #3
  5. Join Date
    Jun 2015
    Posts
    25
    Reputation
    i got this question wrong also. what is the correct answer?

  6. #4
  7. Join Date
    Jan 2015
    Posts
    9
    Reputation
    Thank You secondGen

  8. #5
  9. Join Date
    Jan 2015
    Posts
    9
    Reputation
    Quote Originally Posted by hy3533 View Post
    i got this question wrong also. what is the correct answer?
    Answer is only in corrosive atmosphere

  10. #6
  11. SecondGen's Avatar
    SecondGen is offline
    I push buttons.
    NETA Level III Pro Subscriber
    Join Date
    Jan 2014
    Location
    United States
    Posts
    508
    Reputation
    There is a lot of confusion around this question so hopefully this can add some insight to my previous post. I found this little blurb noteworthy from Square D regarding lubrication, with the key point being that lubricants also prevent corrosion:

    The function of a lubricant is simple - reduce friction between moving metal surfaces. A lubricant coats surfaces and resists being displaced by pressure, keeping the metal parts separated. Lubricants also prevent corrosion, block contaminants and can serve as a coolant. A good lubricant flows easily under pressure and remains in contact with moving surfaces. It does not leak out from gravitational or centrifugal forces, nor does it stiffen in cold temperatures.
    I said before that circuit breaker contacts usually should not be lubricated because it can increase resistance, which is still true, but sometimes lightly lubricating the main contacts with an approved lubricant can guard against corrosion. It all depends on the environment, like a chemical plant for instance.


    Quote Originally Posted by zofofg View Post
    Answer is only in corrosive atmosphere

    Happy to help, zofofg.

    Quote Originally Posted by zofofg
    Thank You secondGen

  12. #7
  13. Join Date
    Jun 2015
    Posts
    12
    Reputation
    thanks this was helpful

  14. #8
  15. Join Date
    Dec 2018
    Location
    Atlanta, GA
    Posts
    27
    Reputation
    Quote Originally Posted by zofofg View Post
    I am new in this industry but am questioning an answer i got wrong on the practice test.



    Obviously you see my answer of "contacts should not be lubricated", could this question be about hinge points that you would oil/lubricate. I asked a Level III I work with and he has never heard of lubricating the actual contacts. Does anyone have any clarification. Thanks in advance
    You apply grease to the contacts no lubrication.

Subscribe

Share this thread

Related Topics

  1. Do You Ever Grease Circuit Breaker Contacts?
    By alexlounsbury in forum Electrical Testing Talk
    Replies: 9
    Last Post: September 28, 2022, 10:41 AM
  2. Contact resistance tester doesn't display any reading
    By lnides in forum Electrical Testing Talk
    Replies: 12
    Last Post: December 21, 2020, 01:32 PM
  3. Draw out circuit breaker positions, how many?
    By Mjeelemco in forum NETA Level 2 Exam
    Replies: 9
    Last Post: December 12, 2020, 07:54 AM
  4. Identify this circuit breaker symbol
    By MAKI2016 in forum NETA Level 2 Exam
    Replies: 10
    Last Post: September 27, 2017, 08:33 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net