    Sometimes we have to test in construction environments and there hardly ever an option for test set power other than on-site temporary. Of course everyone is using power tools, which causes fluctuating voltage/currents back at the test set.

    I know some companies will rent large generators but I am not so fortunate. Only a few of us even have 2kW units on the truck. Just wondering how many of you guys are actually supplied with dedicated power sources when you test, and if not, how do you compensate?

  2. #2
  3. Join Date
    Dec 2014
    Location
    Maryland
    Posts
    14
    Reputation
    Back in the 80's we used to carry Sola isolation transformers to smooth out input voltage. Have not really had input voltages fluctuate enough lately that the newer test sets could not handle it. If we are having circuits constantly trip due to other contractors, generally the electrical contractors we work with are willing to help out with a dedicated circuit.

  4. #3
  5. Join Date
    Aug 2014
    Location
    Capital City
    Posts
    74
    Reputation
    Guess I should have mentioned I'm talking about using equipment from the 80's, lol. The newer test sets do have better power supply's on them that filter input voltage pretty well. I mainly run into problems when using the older Biddle hi-pots. It is very frustrating when you are doing a 15 min withstand test and your test voltage starts bouncing around. A 1:1 isolation transformer is a good idea, thanks for that.

  6. #4
  7. Join Date
    Apr 2014
    Location
    United States
    Posts
    42
    Reputation
    How long have you been in the trade Arnold?


    Quote Originally Posted by ARNOLD ZIFFEL View Post
    Back in the 80's we used to carry Sola isolation transformers to smooth out input voltage.

  8. #5
  9. Join Date
    Dec 2014
    Location
    Maryland
    Posts
    14
    Reputation
    Quote Originally Posted by cjones09 View Post
    How long have you been in the trade Arnold?
    I started during Ronny Reagan's Presidency, When relay test sets weighed about as much as a Smart Car. Circuit breaker analyzers required clamping down a #2 pencil onto a rotating paper drum chart. Doble sets had analog meters (most meters were analog). The oldest relay that I saw still in service was an overcurrent with a lead weight on a chain, instead of spiral spring return. If it was too slow on the curve, file some lead off. If it was too fast, dip it in melted fishing line weights.

Subscribe

Share this thread

Related Topics

  1. Fall of Potential Test - Voltage/Resistance Rises Dramatically
    By BrickSalad in forum Electrical Testing Talk
    Replies: 12
    Last Post: August 18, 2021, 11:18 AM

Tags for this Thread

Follow us


Explore TestGuy


NETA Certification Training


NICET Electrical Power Testing


Help and Support




You are viewing the archives. Enjoy new features and join the conversation at wiki.testguy.net